SMC DASABCIP connection crash

b_e33

Member
Join Date
Mar 2013
Location
lolo
Posts
59
the SMC application (wonderware DASABCIP) connection is ok , but after hours the application cut out and i do not have connection between the INTOUCH HMI and the ControlLogix PLC
how can i fix it?
i try to install again the DASABCIP
but still crash
 
To troubleshoot the issue, I would:
1. Check the HMI can still ping the PLC (i.e. basic connectivity is still in place?)
2. Look through the log files within the SMC to see if any issues are present.
3. Check licencing - I know that if a valid licence isn't installed for DASMBTCP it will halt the IO server after a couple of hours

HTH
 

Similar Topics

I need to purchase a few Large soft starters for our plant and we prefer to stay Rockwell. We have purchased SMC Flex 150 in the past and they...
Replies
7
Views
226
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
Replies
0
Views
336
Hi everyone, We are having Fanuc 16 i CNC system. I need to interface SMC ex260 SEN-1 ethernet valve module with the CNC . Does anyone know the...
Replies
0
Views
367
I am trying to add a TCPIP server group to integrate a Schneider M221 PLC in to Wonderware. When right clicking on the Operations Integration...
Replies
0
Views
438
Hello there, Our plant is running Wonderware Historian on a Virtual Server and every few days I'm losing comms to my PLCs. Usually I can simply...
Replies
3
Views
2,080
Back
Top Bottom