SMC Solenoid bank air control issues
ziyaddin2015
Nov 2019
USA
84
Hi All,
Solenoid bank controls air to 8 cylinders. We used to able to move cylinder up and down by hand no problem but now there is a small amount of air going to those cylinders when they are not energized(retract position). We are going through lot of cylinders on this line in comparison to other similar lines. Please help.
EX250-SEN1 module.
You most likely have blow by on the solenoid. Meaning that the valve is not fully shut when de energized.
Is the air supply lubricated, often without lubrication the seals dry out and pass air, Try putting a little lube into the air supply to the valve & stroke it a few times. You can also do the same for the cylinders. In the food industry you must use food safe lubricants.
check this out
Not sure I have all your info needed to trouble shoot, but if cylinder retracted then air is normally on one side of cylinder, if you have air leaking out exhaust it could be as said above valve is leaking by in de-energized state or it could also be that cylinder seal is leaking by
The cylinders are replaced biweekly and I dont this all eight cylinders leaking but I ll check the exhaust mufflers this week. I 've seen those get dirty which is what might be not exhausting air completely. I ll get back to you with a fix. Thank you all.
I am not a fan of valve banks, one bad valve puts backpressure on all the rest, and the fact that by the time you go to replace several valves they have been discontinued and you are forced to upgrade everything or go to eBay. I know its easier to design when building a machine and probably more cost effective and space saving. But on the maintenance side at 2am its a pain not having the correct valve to install. I have always mounted individual valves for ease of replacement and found the MAC valves so reliable I always use them, with over 250 of them operating on everything imaginable in the dirtiest places.
Hi, I'm new to PLC so really need your help! I'm using Omron CPM2A PLC and trying to control a SMC SY3160 24DC Pneumatic Solenoid Valve. Here I...
8,493
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
314
Hi everyone, We are having Fanuc 16 i CNC system. I need to interface SMC ex260 SEN-1 ethernet valve module with the CNC . Does anyone know the...
358
I am trying to add a TCPIP server group to integrate a Schneider M221 PLC in to Wonderware. When right clicking on the Operations Integration...
425
Hello there, Our plant is running Wonderware Historian on a Virtual Server and every few days I'm losing comms to my PLCs. Usually I can simply...
2,073
