Soft Start means just that!
You normally set the initial current/torque/voltage (depending on mode or model), then the max current/torque/voltage, and it ramps it up.
IF the starter is sized properly for the application, the load will start, as the max amps can be set as high as Locked Rotor Amps...
I've been working with soft start drives since their inception, and I can't recall ever encountering such an absurdly small starting torque limit.
Limiting the starting current limits the starting torque, doesn't it?
This is a snippet from a Rockwell white paper. I can't find anything that shows more starting torque that what is listed here.
https://literature.rockwellautomation.com/idc/groups/literature/documents/wp/150-wp007_-en-p.pdf
@jraef and @Gene Bond - we use these on centrifugal fans and impeller pumps, since they have very low starting torque required.
I know that, in the past, some mines used a fairly complicated setup to start conveyors with MULTIPLE 250 HP motors (to get enough starting torque) and then essentially shut off all but one when the conveyor was up to speed. Is that still done?
I would think that a VFD to start up a constant torque load like a conveyor would make more sense. You can use a bypass contactor to run at full speed after it's been accelerated ... ?
Just for posterity, since this was written years ago and is dropping off of the radar, I suggest that if the subject of how and when to use various starting methods is of interest, download and save this somewhat more comprehensive White Paper. The only way I could find the link now was because I already knew the exact name, otherwise I couldn't find it on Rockwell's site.
It's called "Starting High Inertia Loads: A Comparison of Starting Options"
We still use a lot of them on Crushers, Shredders and Grinders of >100HP.
As far as the big, long conveyors, there are still some out there on soft starters, but VFD's do most of it now, where one is the master and the others are torque followers, to share the load. The biggest issue with multiple motors on 1 load is that the motors really need to bematched if they are fed from the same power source (rather than individually controlled). Otherwise, 1 motor may wind up with the majority of the load.
I don't know if anyone still does it, but a few were using bypass contactors on VFD's if a fan was running at 100%, and then transition back if the demand lowered. It was not as good IMO as the energy saving setting on modern drives, which can reduce the voltage when the load is lighter than 100%.
That's a good paper jref. I somewhere have a similar one written by one of the guys at Saftronics from a good while back (1980?). It did not mention VFD's for obvious reasons back then :) (nobody made an economical and reliable VFD back then)
Thanks for the link. I'll add it to my library of reference material!
Long before that white paper, other engineers devised mechanical means to start those high inertia loads: https://www.youtube.com/watch?v=fNuI6keQXYA
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
329
We have a 5 Ton Rheem A/C unit at home We only run it in the Summertime, and sometimes in the Fall. It does have a habit of blowing fuses at...
18
2,519
I have a customer with an ABB PSE170-600-70 Soft starter running a 125HP Bucket Elevator motor (480V). Its been running fine for several months...
3,328
Hello all i know it isn't a plc question but with time i have seen a lot of knowledge here on motors/drive etc.. When braking with a drive, we...
18
7,731
Hello I'm wondering if it is possible to add a forward/reverse to an already existing soft starter
2,018