Good Morning.
Hey the place hasn't changed a bit.
MCC Cans have two Nema 2 starters, 120 v coils, pick up current 1.91 (cold) holding current is .065
E-300's have (3) 3 amp (@120v) solid state relays, I have two E-300s in a dual motor MCC. Rewiring to create a double redundancy for overload and control.
Using the first unit, r-14 and r-24 to eneregize each of the starter contacts.
Using second unit to energize motor "A" or "B" in the event of a single motor failure.
This would create a 120 v @ .065 continuous back feed on either of the first units SSRs
Checked internet, checked Rockwells knowledge base and forum.
Best I have gotten is twice the current rating of the SSDs of the back feed (maybe) .
I do not see a leakage or doping issue, Can anyone clarify with first hand experience any short or long term problems created by this configuration
Your time and attention is appreciated. Thank you
Hey the place hasn't changed a bit.
MCC Cans have two Nema 2 starters, 120 v coils, pick up current 1.91 (cold) holding current is .065
E-300's have (3) 3 amp (@120v) solid state relays, I have two E-300s in a dual motor MCC. Rewiring to create a double redundancy for overload and control.
Using the first unit, r-14 and r-24 to eneregize each of the starter contacts.
Using second unit to energize motor "A" or "B" in the event of a single motor failure.
This would create a 120 v @ .065 continuous back feed on either of the first units SSRs
Checked internet, checked Rockwells knowledge base and forum.
Best I have gotten is twice the current rating of the SSDs of the back feed (maybe) .
I do not see a leakage or doping issue, Can anyone clarify with first hand experience any short or long term problems created by this configuration
Your time and attention is appreciated. Thank you