Solution for Trapped Key Safety Upgrade
mc62182
Sep 2016
USA
HI guys I wanted to get some ideas. I am trying to figure out a way to lock out a machine with a trapped key setup that isolates power and drops out an MSR then only unlocks the doors when the key is removed then also somehow requires the operator to take the key without using an exchange station. The customer does not want to make the operator walk around to an exchange station but still ensure the key is a requirement to unlock the machine.
I have read alot of manufacturer info but don't think this is a possibility as the trapped key when turned off and removed would need a set of contacts or some other means to initiate a door unlock signal.
Any ideas?
Thanks, I have used the Fortress before but the customer is asking for no exchange station and only wants the one key on the HMI panel. I really don't know if it can be done the way it has been proposed.
The 440T AB rotary switches can isolate power but there is no requirement to remove the key unless you have an exchange station as mentioned.
Any good ideas with other relays or switches to the circuit? I'm just trying to think outside the proverbial box here.
Hi I am unclear of your exact needs but I would
1. Stick to certified devices (cover your a$$)
2. Call a vendor such as fortress, if they don't make it, it is unlikely it is available
3 Does the customer have a similar set up at their plant you can go and look at?
4 Just because someone asks for a solution it doesn't mean it is the best or safest one
Good Luck
Any ideas?
You don't have to have an exchange station.
You can exchange the key at the gate entry point
The "A" key is at the operator control station (key switch), the "B" key is removed at the gate entry lock
Does this picture help?
Its true that the B key does not have to be removed BUT it does have to be rotated to unlock the gate.
If the operator does not remove the key, then isn't that just a training/procedure issue
Something doesn't sound right.
Let's say you use solenoids to unlock access if the key is turned. If the operator is the only person working on the equipment, then wouldn't they have to walk around the machine even if a key is not required to unlock the door? So, they wouldn't be saving any effort there.
Now, if more than one person is working on it. It would save walking around the machine. Of course doing so would be very dangerous because the person exposing themselves to danger isn't in control of the equipment.
It comes back to the hazard analysis. You could have the trapped key both disable power and unlock the doors. But know you have to consider what if the operator doesn't take the key and someone else comes along. If you force the operator to take the key that isn't an issue.
The weakest link is always the operator maintaining sole control of the key.
Hello everyone, I'm working on a project that involves controlling an array of nozzles within a CNC environment, where the nozzles travel along a...
186
Our plant has a network repeater station located in a field with two ProSoft RLX2-IHG network radios for connecting our plant network to a well...
2,415
Hello. This is one for the Mitsubishi experts. I need to measure the time for a remote device's to return process data sent from the i-QR...
17
2,136
Hi all, I have a customer who wishes to to display some of the information from their refrigeration plant (CompactLogix PLC on Ethernet/IP) on...
1,520
Hi Guys, I developed HMI with Resolution of 1920 x 1080 in FactoryTalk View studio SE; and also use same resolution for Client Runtime PC yet...
559