Some Dont shows in OPC Test Client
bornwild
May 2010
Riyadh
429
Hello all,
I have a compact Logix CPU communication with Rslinx. Scada is Wincc is pulling tags from RSLINX OPC server. It is a working machine and now I am trying to add a few tags on the WinCC. I have added Real data types in the PLC and I can the the data in the OPC test client software. For some reason Bool tag doesn't appear in the OPC test client so I added a real type tag but for some reason, they don't show up in the OPC test client. Is there something I need to do for the tags to show up. All I am trying to is put these data on my WinCC HMI. Any help would be appreciated
I got the see the value in the OPC test client. How do you which data type to use . It is a bool in the PLC. When I select VT_bool in the opc I see 'off' not 0 but when I select VT_R4 I see 0. If am trying to read this tag from OPC to Wincc and do some scripting based on this tag. However I don't know which data type I should use. Technically it is Bool but for some reason rslinx OPC treats as different type. Can some one help
Hello Bornwild: Not sure if I understand your question. The OPC Client is reporting the items as VT_bool data type. I ahve not used Wincc but you should be able to treat VT_bool values of ON and OFF just like 1 and 0, respectively.
I may not be fully understanding your question.
finally got it to work. My bad, in the PLC address in the Wincc I missed the connection name and wrote only the tag name. Silly mistake
Hi; First of all, I am sorry that my post is not relevant with this forum. I have recently purchased Samsung cell phone. I have alreay saved...
77
Hi I am in the process of making an OT lab for training and to test incident response, an i keep hearing NOT to scan network because some...
897
A MELSOFT application error has occurred. Please restart. <ES:020000006> Why Occur this message? I'm try connecting to USB Pls Help me..:shock:
2,038
I have a Delta DVP 16EC PLC and does not have a RUN-STOP button I can make it go into RUN with the PC in the simulation and everything is perfect...
2,008
Hello, I'm running my Plc in PLC Simulator (Unity Pro XL). Intouch sees the connected links but the tags are not matching (+1 on InTouch)...
1,250