I'm preparing to run several large 10,000 CFM squirrel cage style blowers, each with its own VFD, and I am concerned about the regenerative amperage from the motor when stopping. I'm well set up already with full access to all parameters and have verified rotation, I just want to prevent problems.

Does anybody have any recommendations about how to correctly set these up - parameters to address, configuration, etc.?

Steve
 
Dynamic Braking if the provisions exist.
Regenerative type VFDs with properly configured RAMP rates if feasible.
If not, STOP by COASTING.
 
Last edited:
If the process permits stopping by coasting is certainly a viable way to go. You can always add DC injection braking at the very end of the stop cycle.

However, the high inertia can still cause problems during normal acceleration and deceleration during speed adjustments. You will probably have to adjust the accel and decel times to prevent trips. If accel is to short you will have over-current trips, and if decel is too short you will have over-voltage trips.

I've noticed that the ability to handle high inertia loads varies significantly from VFD brand to brand. Cutler Hammer seems to handle them well, GE poorly, for example.
 
The process is really very forgiving so coast-to-stop is not a problem. Same for accel-decel times. To start with, I am thinking 10 seconds to accel and 60 seconds to decel.

One other concern is restarting while the motor is still coasting. My understanding is that this can cause problems and, if memory serves, the AB PowerFlex 70 has a parameter to account for this - I don't remember for sure. I'm on the hunt for that now....

Steve
 
I agree with Tom about the manufacturer choice.
A-B is somewhere in the middle.
ABB is on the top of my list when it comes to high inertia, VFD driven loads.
 
Being to start into a spinning load is called different things by different manufacturers. Not sure on AB.

Look for something called Flying Start, Catch a Spinning Load, or similar.
 
Thanks DickDV - that is the one I was looking for.

FYI - in AB its called "Flying Start En" and is described as "Enables/disables the function which reconnects to a spinning motor at actual RPM when a start command is issued."

So:

Coast to Stop
Long Accel & Decel times
Flying Start En = Enabled

Steve
 
With A/B drives, it has been my experience that using Flying Start Enable can cause a brief delay, and even a short period of (slow) reverse operation when starting from a fully stopped condition. The delay was about 1-2 seconds in my case. Make sure the blower can tolerate that before using it.
 
Ok. Good to know.

When you say "be sure the blower can tolerate", do you have anything specific in mind? In my application, slow reverse rotation for a short time shouldn't be an issue for the overall system, but is there some kind of damage to the motor or blower itself you are thinking of?

Steve
 
Nah, in my case, it wasn't a problem either with a belt driven blower. The tensioner was spring loaded so it "didn't look right" seeing it reverse according to one of the techs watching the blower on the roof. It hasn't been a problem with that feature enabled and it has helped reduce faults when the wind is blowing (90% of the time here) and the blower is moving when starting.

On a conveyor application, however, it was a potential problem, so I had to leave it disabled.
 
Last edited:
Okie

If the drive is set to Unipolar for direction command and reverse is disabled does it still do this? It should not.

We have one where we change the revese enable / disable from the plc so it can be run in revese in the hand mode. Forward only in auto.
 
Last edited:
Most drives with Flying Start enabled and Reverse blocked out will still find a spinning motor that is turning backward and bring it back forword. OkiePC is probably seeing the drive search forward and backward to find the motor and while doing that the motor drifts back a little too.

This would be a big problem on loads that have any kind of reverse rotation device installed, such as a sprag clutch or one-way clutch or a ratchet as on some conveyors.
 

Similar Topics

im controling a lenze inverter using an s7 314-dp connected to it through profibus i have the application where im goin to gear this motor to a...
Replies
0
Views
2,342
Have not given up on quest for 3 phase drive on electric vehicle. Have another thread "electric vehicle" Have a vendor for the controller...
Replies
20
Views
4,361
This is slightly OT, but I figure it's something we deal with when building control panels. Does anyone know of a top-entry, spring-clamp...
Replies
5
Views
4,235
im a lil confused about the difference between servo motor and ac squirell cage induction motor. they both have encoders.and i i saw applications...
Replies
9
Views
6,982
I'm sorry this may not be directly related to PLC but can anyone recommend someone that makes good cagemakers? (Preferably auto-weld too)
Replies
4
Views
1,498
Back
Top Bottom