I have station PLC S7 400 connect with ET200. And I have a question: if ET 200 occur error: loss supply. I'm not sure, all station PLC stop?
 
agree with jesper. at least it would be desirable to read the error and perhaps to log it (and show it on HMI).
if these OBs are needed (ie PLC shouldn't go to stop on profibus error), then the alarm when the error occurs (and is bypassed) is welcomed.
 
In my opinion, at the very least the error OBs should contain code to generate alarm messages.

Correct. All blocks can contain code for generate alarm, but it depend of the application / plant.

If the blocks don't have code the PLC will not stop at ET200 error, and no alarm is generated.
 
Correct. All blocks can contain code for generate alarm, but it depend of the application / plant.

If the blocks don't have code the PLC will not stop at ET200 error, and no alarm is generated.
Exactly - I'm fairly certain that's jesper's point. An error shouldn't just be bypassed. It should at least generate an alarm
 
Thanhks all for anwser,

I agree OB87 (Communication fault). But, I don't know write program in OB87 for interrupt ET200 station error.
 
Thanhks all for anwser,

I agree OB87 (Communication fault). But, I don't know write program in OB87 for interrupt ET200 station error.

Hello plc_cnc;
OB 87 will not help you for your problem. The ET 200 is considered a Profibus slave station, and will cause OB 86 to be called when it loses contact with the DP-master.
look at Jera's earlier post, suggesting to Use OB82, OB83, OB86 and OB122. Just add these to the programming blocks and download to the CPU, then open the diagnostic buffer of the PLC when the SF/BF LEDs become active to locate the source of the error.
Hope this helps,
Daniel Chartier
 
Thanks DChartier,

I'm not sure. After ET200 occurs error, S7 400 station still run if I use OB82, OB83, OB122,
 
Hello PLC-CNC;
Look at chapter 23 "Diagnostics" of the following manual:
Simatic : Programming with Step 7 v.5.5
You will find a description of all the diagnostic OBs, individually, with information such as this one:

If you do not program (note: this meand created and loaded to the CPU blocks) OB86, the CPU changes to STOP mode when a rack failure is detected.

If you look at it another way, the statement means that if OB86 is loaded in the CPU and a rack failure occurs, the SF and BF LEDs will light up, but the PLC will not go to STOP mode.

Hope this helps,
Daniel Chartier
 

Similar Topics

Has anyone used a Red Lion data station plus to talk to a micrologix 1400? If so, did it work OK or are there any issues I need to be aware of?
Replies
4
Views
5,103
Hi guys, I am caught in a situation where I have no choice but to do a upload. This is what I get from the help file: Restrictions when...
Replies
2
Views
4,388
Hi, I want to build a demo station to test devices and programs and I need some help with it. I want to connect GuardLogix, Piltzmulti and...
Replies
1
Views
149
Hi, I'm trying to export data from a DataGrid to Excel using VBA, but I'm getting an error "Object doesn't support this property or method". The...
Replies
0
Views
82
Hello, I have a CNG compressor that is run by a PLC. I tried to get team viewer on it to be able to view it remotely, I accidently disabled the...
Replies
0
Views
109
Back
Top Bottom