I'm new with siemens step 7 (PLC : S7 300) and i have a question about using pointers.
I have created a 5 DW shift register for an conveyor which is clocked by a puls generated bij the conveyer. At a on a control panel specified starting point (example : bit 80 of 160) i have to make an action.
I want to make a pointer where the initial value is te starting point of the register then add the value specified on the control panel and see if that bit is '1' or '0'.
Can anyone help me with this problem?
I dont know if this is what you are looking for......
//Open db containg databits
OPN DB 1
//Load startingpoint in adressregister1
LAR1 P#DBX 0.0
//Load value of MW0 into accu1 (Integer value from Op)
L MW 0
//Add value from MW0 to adressregister 1
+AR1
//Check if bit is 1
A [AR1,P#0.0]
= M 2.0
If MW 0 in this case contains 8 bit 1.0 in db1 is checked. If mw0 contains 25 bit db1.dbx3.1 is checked.
Thanks Bratt after some modifications i think it will work.
We'll see at next weeks tests anyway.
pointer
there are many solutions ....
L MW 10 // your bit index value 0..159
LAR1
OPN DB xx
A DBX[AR1,P#4.0] // assuming your DW's start at 4.0
= M10.0
hope this helps you
Hello! have a related question about pointers on shift register applications..how do i write the value of a particular bit say M0.0 in the shift register(5 DW )using pointers and read its value after say bit 80?
I have a basic understanding of truth tables and the addresses. My issue is that for every letter that I have to make, I need a truth table that...
1,452
I have for the longest time avoided using the S7-1500 because everyone warned me that TIA portal was a stinking pile of garbage to be avoided at...
25
12,244
Good Afternoon , I have a project that I am beginning , that I will be using 3) PowerFlex 525's drives. I took notice of the StepLogic feature...
3,925
So I know that in RSLogix 5000 you can use a tag in place of a static number in an argument of any instruction. For example... If I wanted to...
3,481
Dear Experts. I have one project using HMI Ktp 1500 comfort and S7-300 CPU 315-2DP. The HMI KTP is using Software TIA porttal for programming, and...
2,041