Strange jumper between elements

With 2 separate 50V transformers that jumper would keep the center potential to ground equal between the 2 circuits. And hopefully very close to 0V to ground. Myself I would ground that connection - and maybe it is just didn't make it to CAD.



Otherwise if the resistance of one top element becomes different from the other top element (or bottoms) there could be a potential voltage between the 2 that might be enough to be felt by an operator or technician.
 
I presume that transformers have 50V and 0V on secondary side, not +25V, -25V. And yes as I_Automation mentioned it should be grounded. Otherwise it is error. Even having transformers in parallels with enough difference in wire/busbar resistance is error.
 
I presume that transformers have 50V and 0V on secondary side, not +25V, -25V...


I've encountered quite a few machines with a floating power source, especially relay based stamping press controls with un-grounded 120VAC.


The relay coils on these controls are in the middle of the rungs and the 2 sides of the transformer output are +60 / -60.


If this was 2x 24V heaters in series on a (slightly overpowered) 50V supply then none of the transformer output leads would be grounded. I'm still guessing the center jumper IS grounded, just not shown on the schematic.
 

Similar Topics

Hello all, I am facing an issue with my Commander SK that I cannot solve on my own, I am struggling on it since several days :confused: The...
Replies
9
Views
1,051
Hi. I'm doing an upgrade of an old 1400e to a new panel view plus 7 standard using ftv studio v 12,which will be communicating to a slc 5/04 via...
Replies
15
Views
2,630
We have an OPC server getting data from a Compactlogix PLC. The PLC also communicates with a Panelview and a couple VFDs via Ethernet/IP...
Replies
3
Views
1,165
I have a small system controlled by a Siemens S7-1200 PLC. I created a totalizer function block (TIA v17), where I'm counting total revolutions...
Replies
16
Views
3,137
I am currently wrapping up a startup of a couple lines of equipment in Asia. Cabinet has A/B 1873-US6T2H unmanaged switch with 6 copper ports and...
Replies
5
Views
1,138
Back
Top Bottom