Actual field case of stray voltage/current for comments...
A PLC relay contact output is to energize the coil
of a pneumatic solenoid. This solenoid is a dual coil,
4 way valve, the type used to extend and retract a
cylinder.
With the PLC output OFF, approx. 28-50 volts AC can be
measured across the coil. [Attaching a small test load reduces,
but does not eliminate the voltage.]
The symptom is that when coil 'A' is attempted to be
energized, coil 'B' is seeming to hold the spool of the
solenoid sufficiently that coil 'A' never gets control
of it. (The same symptom is NOT true when 'B' is attempted
to be energized...'A' does not hold the spool)
The solution was to replace all the field wiring with
twisted shielded wire, and ground the shield at the
solenoid base.
Facts of the case:
1.) The solenoid's rating is 120VAC, 8.3 VA & 67VDC, 8 watts.
2.) The solenoid reads ~890 ohms with a digital multimeter.
3.) The total length of wiring run, from PLC output terminal
to solenoid coil is 3 meters.
4.) Operating voltage is 121 volts, AC.
5.) Solenoid is new; installation is new.
Q1: Has anyone ever seen solenoid coils dual-rated for both
AC and DC? What must they look like inside????
Q2: What the heck...how do you avoid this kind of problem
in future designs?
A PLC relay contact output is to energize the coil
of a pneumatic solenoid. This solenoid is a dual coil,
4 way valve, the type used to extend and retract a
cylinder.
With the PLC output OFF, approx. 28-50 volts AC can be
measured across the coil. [Attaching a small test load reduces,
but does not eliminate the voltage.]
The symptom is that when coil 'A' is attempted to be
energized, coil 'B' is seeming to hold the spool of the
solenoid sufficiently that coil 'A' never gets control
of it. (The same symptom is NOT true when 'B' is attempted
to be energized...'A' does not hold the spool)
The solution was to replace all the field wiring with
twisted shielded wire, and ground the shield at the
solenoid base.
Facts of the case:
1.) The solenoid's rating is 120VAC, 8.3 VA & 67VDC, 8 watts.
2.) The solenoid reads ~890 ohms with a digital multimeter.
3.) The total length of wiring run, from PLC output terminal
to solenoid coil is 3 meters.
4.) Operating voltage is 121 volts, AC.
5.) Solenoid is new; installation is new.
Q1: Has anyone ever seen solenoid coils dual-rated for both
AC and DC? What must they look like inside????
Q2: What the heck...how do you avoid this kind of problem
in future designs?