Studio 5000 Totalizer Function Block GPM to MGD
jfritz8
Mar 2016
USA
I am trying to setup the TOT function block so that I bring in GPM and want to output MGD. I cannot seem to figure out the correct gain in the function block. I typically use GPM and convert it to Gal x 1000 using the gain, but I'm not sure if it's possible to get MGD as the totalized output. Has anyone ever tried to do this using the TOT function block?
Currently it is set for 1 second (1000 ms). I've found that converting the GPM number to gals per day then using that as the input, setting the gain to .00000144 seems to work. But I was hoping to not have to do that conversion elsewhere in the program.
How are you converting GPM to [gals per day]?
that's what I thought.
So if the reading is, oh, say, 1440GPM, you divide that by 1440 to get 1.000GPD?
What seems to be missing is a sense of proportion ...
So that's what I'm trying to figure out. Ideally I would like to keep it at GPM in the totalizer and output Million Gallons per Day.
I am taking the GPM and DIV by 1440.
Okay, so you have a flowrate of 1440gpm, that is one thousand four hundred forty gallons every minute, and you think if it keeps flowing at that rate, over a thousand gallons per minute, minute after minute, for a full day, that it will accumulate but one gallon over the course of that day (1.000GPD).
Does that sound right to you?
I think that you are confusing flow rates with totalization. A flow rate of 1 MGD = 694.44 GPM so if you were to flow at 694.44 GPM for 1440 minutes (1 day) you would end up with a totalized value of 1 million gallons for the day. If you want the totalizer to read how many millions of gallons have been produced for the day then probably the easiest would be to divide the GPM reading by 694.44 and feed that into the totalizer at give it an appropriate rate. Unfortunately its been too long since I attempted to do this in AB I can't give a good answer for what the rate should be.
As you point out, flow RATE is the volume per time. It can be gallons per minute, or million gallons per day, acre-feet per fortnight, or ......
A flow TOTAL is just volume. If you multiply any flow rate by the elapsed time interval at that rate and add it to the previous total volume you will get the volume accumulated over the time elapsed since initiating the totalizer.
The easiest way to do this is to totalize as gallons and then divide by one million to get totalized million gallons. This will NOT be mgd, except at the very end of the day.
Good morning, I have a flow meter that has an output pulse configured to 378.541 liters per pulse. My question is, do I just count the pulse per...
19
1,889
Good morning, I have a flow meter that that has an output with is a pulse. The pulse is configured to 378.541 liters per pulse. My question is...
746
Hello everyone, I'm new here, I hope someone can help me. I've been trying to install EDS files to my Studio 5000 with the EDS tool installer but...
117
Hi Everyone, I am facing an issue while installing the STUDIO 5000 in my windows 10 PC. During installation I am getting an error that " Error...
185
I am connecting to a remote device. When attempting to upload I receive an error that states: Error: Auto_Functions: The Import was aborted due...
187