Surge Protector and Control Panel UL508A
RRoc
Jan 2017
California
45
I am using a Phoenix Contact Surge Protector. See data sheet attached. It's ULRecognized. My PLC Control Panel has to be UL508A. I'm pretty sure this part would be ok use if I am to UL my control panel.
The Engineering Company reviewing my Panel drawings is wanting confirmation that this part meets UL508 requirements.
Is this part ok for what I am doing?
UlL 508A documents list, in the back, all of the other UL listing numbers that are allowable. If the SPD is listed or recognized under one of those acceptable file numbers, then you can use it.
As a recognized component, you must "add it to your procedure" which entails investigating why it is only recognized and not listed. That is usually the result of it requiring something else as part of an assembly that you as the panel builder must demonstrate and document has been provided and properly applied. In the case of SPDs, I've found that usually means they must be fused with a very specific fuse.
If you are a UL508A shop, I'm a bit surprised that you would need to ask this question though. If you are not, why bother asking? You can't label the panel anyway.
Every I/O Analog and Discrete needs a surge protector in my control panel. We have alot of I/O and the Cost for the Phoenix Contact Plugtrabs is...
25
9,811
Hey guys, I have a machine going to Mexico and they're requesting me to put a Surge Protector/Filter on the secondary 120vac of my 5kva...
3,019
Dear all, In one of my project, the client spec required us to put lighting protector for all the incoming cable from another block of building...
2,222
Can anyone recommend a surge protector to install in a controls cabinet (non-ventillated) inline feeding the power supply (P-2 I think) of a...
3,319
Hello all, As the title says I am looking for some information on some inline 110 VAC surge protectors. Something that is compact in size and can...
5,483