Skiroy
Member
It has come to my attention that the old PLC-2 system was Tric outputs so it did not matter. We have a Micrologix 1400 PLC with add on I/O modules which do not come in TRIACs and only have Relay outputs for 120ACv. Anyways I had to come up with a solution to protect the life of the outputs due to high inrush currents and backwards current, due to the pneumatic valve inductive loads. I had looked into AB solidstate relays with surge suppressors built in which would be perfect unfortunately it would cost $1600.00 to do this and there is no way Im am going to convince my boss to shell this amount of money out.
Now I know this can be done with running MOVs in parralel with the load(pneumatic valves).But I was told that you should not wire these at the modules or PLC,but that they should be wired at the load. But at the load ,would mean splicing a MOV into wires in the conduit cable that runs into each Pneumatic valve manifold. This seems odd,sloppy and unsafe to do and I would think that it can be done in the panel, in a clean way. And MOVs are a heck of a lot cheaper than the AB interpolasing relays which I was earlier refering to, as the solid state relays with the surge protection.
1. Any suggestions on this?
2. Do MOVs cover both backwards current(collapsing inductive load) and high inrush current issues or just one or the other?
3. How would I figure out the rating of the MOV I would need for a load(In this case a .36A 120ACV valve)?
Thankx
Now I know this can be done with running MOVs in parralel with the load(pneumatic valves).But I was told that you should not wire these at the modules or PLC,but that they should be wired at the load. But at the load ,would mean splicing a MOV into wires in the conduit cable that runs into each Pneumatic valve manifold. This seems odd,sloppy and unsafe to do and I would think that it can be done in the panel, in a clean way. And MOVs are a heck of a lot cheaper than the AB interpolasing relays which I was earlier refering to, as the solid state relays with the surge protection.
1. Any suggestions on this?
2. Do MOVs cover both backwards current(collapsing inductive load) and high inrush current issues or just one or the other?
3. How would I figure out the rating of the MOV I would need for a load(In this case a .36A 120ACV valve)?
Thankx