Read relay specifications closely ...
If the "781" you are referring to are AutomationDirect offerings, be aware what loads you are switching, see page e27-21 under Service Life http://www.automationdirect.com/static/specs/78relays.pdf . They are rated at 200,000 cycles resistive but only 1,000 cycles inductive when you read the "*" note at the bottom of the page. They added this to the specification in 2006 after I installed 6 dozen of them in 2005 and then started having random "control problems" that went away once the 781s were replaced.
YMMV, just my $0.02.
I always install interposing relays on all solenoid valves. If something goes wrong you destroy a $6 relay not the PLC output and the 781 relays are less expensive to replace than fuses.