Talking to a Motortronix XLD Soft Starter using a MVI56-MCMR
May 2017
Regina
I am very new when it comes to programming thing using a Prosoft card using Modbus. I am fine to figure that out by studying the manual. However I cannot seem to find good information on what kind of hardware I will need to get the two devices to talk to each other. We have a similar system with a SLC rack that uses a rs232 to rs485 converter (isolated i believe, it has its own power source) and then two wire 'daisy chain' to each of the devices. I am just trying to get my foot in the door with testing communicating over modbus with a single device for the time being before getting any permanent wiring.
The XLD soft starter uses Modbus RTU protocol over RS-485. You need the info from their manual giving you the Modbus Resister Map to be able to communicate to it. I believe this is a separate manual, it's not in the general instruction manual (last time I checked). In that manual they give you the standard Modbus RTU data packet format that you must use in the other device. How you write communications commands in the other device is going to be part of that device's instruction set.
You may have to call them for it though, I just looked on line and it's no longer there I think because the XLD series is now "legacy".
Hi All, Got a funny issue. I have a 1756-L85EP and a 1756-EN2TR in the same chase. The client asked for the Ferrari and the 3 lane highway!!! We...
182
Hello friends, I am tasked to get a SVX9000 Eaton VFD to talk to a plant which uses Proficy Machine Edition (PAC systems RX3I) PLC. The VFD has...
1,875
What is required for a ControlLogix PLC to read/write tags from a Schneider PACDrive LMC PLC? Does the PACDrive have Ethernet/IP protocol built in...
1,764
Hi Guys Moments ago I just had my first ENBT failure. While the front of it showed everything was fine, it would not respond to ping or to comm...
1,352
Hi, I have 6 SLC 5/02s on 485 network. One of the processors faulted. I've replaced it and downloaded the program into the replacement using the...
1,639