Hello friends, I am tasked to get a SVX9000 Eaton VFD to talk to a plant which uses Proficy Machine Edition (PAC systems RX3I) PLC. The VFD has an OPTCQ card I installed. I have done this using AB ML PLCs but never with a GE. Any help or examples?
Best regards,
JF
The OPTCQ card allows the VFD to speak Ethernet/IP, which the RX3i does not support.
The Eaton OPTCi card supports Modbus TCP communications which the RX3i speaks natively. You're best bet is to swap out the comms card on the VFD to OPTCi so the PLC and VFD can communicate directly, or else you're looking at getting a third device for protocol conversion.
Decent summary here on how to set up the RX3i for Modbus TCP communications: https://www.reddit.com/r/PLC/comments/a3hqcw/configuring_a_ge_rx3i_as_a_modbus_tcp_client/
Thanks much for the help. I cannot find much support from GE. Brino: I do believe the PLC has an ethernet card installed though, which we monitor through Ifix and SCADA.
Beware the difference between:
Ethernet TCP/IP - which is a set of general standards for devices to communicate on an ethernet network
AND
Ethernet/IP - which is an object-based communication protocol developed by Allen-Bradley/Rockwell for devices to communicate on an ethernet network.
The Ethernet/IP name has caused countless hours of confusion over the years, I'm sure. Just because a device can communicate on an ethernet network does not mean it supports the Ethernet/IP communication protocol.
See here for more detail: https://www.rtautomation.com/rtas-blog/ethernet-ip-and-tcp-ip/
I'm getting frustrated creating arrays of variables in Machine edition. I need to make 2 variable arrays that are 102x2 in size, with varying...
112
Hi, I am still a beginner with PLCs and I have never worked with GE PLCs before so looking for some help. I am using GE Proficy Machine Edition...
1,383
I am trying to download version 9.8 of G.E.'s proficy machine edition, does anyone have a link to a download site?
5,196
Need to learn a few more tricks in Proficy Machine Edition. I don't use it often, but one of the first things I usually do when getting into a new...
1,032
I have a GEFanuc plc 90-30 that has dumped it's program and IP. The tool in PAC for setting a temporary IP is not available. The Offline Commands...
2,026