784
hi i have a problem on a machine it is controlled by a automation direct plc 205 with a touch screen(rsview 32) the problem i am having is the temp on the screen is not moving it is 82f all the time is there a way to see if i am getting a signal back at the plc? i am not very good on the automation stuff.
thanks for your time
stu
Stu,
Yes, you can check the temperature signal at the DL-205 Input terminal block. How you check it depends on what type of signal it is. If it is a thermocouple, you need a milivolt meter. If it is from a signal transmitter, it is probably a 4-to-20 milliamp signal, in which case you need an ammeter with a miliamp range.
If you have access to the PLC program, you can also look inside the program to see if the signal level is changing, although this is not easy on an Automation Direct PLC.
First, make sure your PLC is still running. Check the RUN LED to see if it is on. It could have faulted or lost its power.
We have a small plastic parts oven (SP at 210F). It used to have an old bimetal temperature regulator. We are upgrading it using two temperature...
1,535
Needing some help. I have a machine that was put in storage and has ended up in my lap. It had a 5/02 originally but the card was pulled and I...
1,416
I'm tasked with replacing a process's temperature controllers (which feature PID autotuning) with PLC control. Do any PLCs feature PID autotune or...
33
10,234
Hello I have DTC 1001 and DTC 2001 delta Temp control connected to together as one unit , and this unit connected to SS2 plc via Rs485 , My...
1,036
We are currently running 3 point temp control of a kiln and recently had a thermocouple failure which caused issues with our heat up cycle. In...
2,338