test the RSLogix500 code matches with PLC ??
leonlai
Jun 2011
WA
96
Hello everybody,
I'm new in PLC and I have a chance to hand on a PLC system; however, my Boss give me a Laptop with a folder of many PLC code and a system with micrologix 1500; I can connect them and make a communicate of PLC and Laptop;
However, I don't know what code in Laptop is the one the PLC is running and I dont want to overwrite the wrong code to PLC;
How can we test the code in PLC matches with the code in RSLogix 500 ????
In RSLogix 500 under 'Tools' use the 'Compare' function. You can find differences in ladder logic or data tables. Differences in the data tables may be of less importance unless it is critical recipe information for example.
THanks for you quick reply,
I am on the PLC now, under the Tool is Compare, however it not available to click on may be because my RSlogix code is offline; But when I try to open one file code and click online; it pop up a "Going to Online Programming State" windows which has Seaching for Offline Image: No matching Found and has three option: "Cancel"; "Create New File" or "Browse"; SHould I click "create new file" ? will that overwrite the code in Micrologix ???
It's a RSLogix500 v 8.10 (CPR9), I just open the file that I suspect it would be the one in Micrologix 1500; It's not online yet; then I open the "compare" but it greyed out ! Dont wanna go online because afraid it will overwrite the Micrologix code
from what I read from rockwellautomation.custhelp.com/ci/fattach/get/31854/1259762809.
r Comparetool to compare 2 offline code ??? any help ?
Open RSLogix. With no program go online and upload the existing program, save it under a new name, and then compare the two programs.
You can also check the Processor Name and see if that matches.
In RSLinx, you will see the name of the controller you're connected to, and you can compare that to the name in the program (Left side, "Controller", "Controller Properties")
That might help you weed out a few, or lead you in the right direction.
what different between download and upload ? is it download is from RSlogix to Micrologix / upload is from Micrologix to RSlogix ?
Thank you guys for helping;
In RSLinx I saw the Micrologix name is LS-25; that match with the name of one of the file I have. I just want to make sure and learn a new way to compare with the code in Micrologix
ANother problem is just pop up ! why when I go online and upload from RSLogix with no program first, it load the code and I see no description like the one I have in my laptop ? two files are the same; one in my laptop (*.RSS) has description like ON_OFF_ALARM while the one I go online has no description ????????
Very few PLCs store descriptions, comments, and similar documenttation in the PLC. That is part of the logic files on the PC hard disc.
The compare function does not compare the documentation - only the logic.
Hi, I am using M221 reading from 3 different sensors (modbus rs485) sharing same bus (daisy chain). I am currently using READ_VAR (in total...
88
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
191
See code at the bottom. Hi all. For the story, this is my first complete project using a Rockwell PLC, I've been mostly working with Unity Pro...
801
My question is regarding the number of Test outputs vs the number of inputs in a module. In the case of a 1734-IB8S card, there are 4 test...
1,202
Hi, I have to test a control logic that required to change the input temperature as the process variable from thermocouple transmitter on the...
627