Test
randy
Supporting Member
Apr 2002
158
I’m taking an evening class at our local community college. The course is Industrial Electronic Control Systems. My instructor kind of veered away from our topic that evening, which was Process Control Methods, and got on to PLC’s. He worked out a PLC logic program on the blackboard, which he was using one momentary push button to activate a discrete output and using the same button would de-activate the same output. He was trying to manipulate the scan sequence, which is from top to bottom, left to right. He worked out the problem on the board and at that time it did seem to make sense, but I was not 100% sure.
I have a Mitsubishi FX2N PLC at home to practice on in my free time. So I went home to try his logic on my system. This did not work and before I confront my instructor, which I have not received my grade yet, I want to be sure. Please review the logic and please tell me what I am missing…
--[PB1]--[M1/]----------------------------------(M0)
--[PB1]-----------------------------------------(M1)
--[M0 ]--[M1]-----------------------------------(M3)
--[M0]--|--[M3/]--------------------------------(Y0)
--[Y0]--|
What it boils down too is that M0 cant energize Y0 because M1 is on after MO which basically turns off M0 before rung that energizes Y0
I think you will find that this would work for using the same switch
to turn an output on then off
--[PB1]--[M2/]----------------------------------(M1)
--[PB1/]-----------------------------------------(M2)
--[M1 ]--[M3/]-|---------------------------------(M3)
--[M3 ]--[M1/]-|
--[M3]-------------------------------------------(Y0)
There are a bunch of ways to do this. How about this one?...
(enlarged for your viewing pleasure) ;)
PB1 M3 M2
---| |-----|/|-----| |-----(M1)
PB1 M3 M1
---| |-----|/|-----|/|-----(M2)
M2 |
PB1
---| |---------------------(M3)
M2
---| |---------------------(Y0)
Output Y0 will change state each time PB1 is pressed
(Copied from a working program, so it's valid) :D
-Ericbig
I do this by using a counter. The momentary input increases the counter by 1. Then just use the bit in the counter that is true when (counter val=1) for the output status. The counter resets its self to 0 after the second press of the button (counter val = 2). You do not need to use any latches as the output will consantly relect the value in the counter. This only requires 3 lines of ladder logic.
Hi
A point of interest for Mitsi FX programmers is the ALT instruction. This is a predefined way of using a momentary pushbutton to toggle coil states. Saves all the other grief.
Chris
Hi, I am using M221 reading from 3 different sensors (modbus rs485) sharing same bus (daisy chain). I am currently using READ_VAR (in total...
101
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
206
See code at the bottom. Hi all. For the story, this is my first complete project using a Rockwell PLC, I've been mostly working with Unity Pro...
811
My question is regarding the number of Test outputs vs the number of inputs in a module. In the case of a 1734-IB8S card, there are 4 test...
1,240
Hi, I have to test a control logic that required to change the input temperature as the process variable from thermocouple transmitter on the...
637