Textile Mill Warper ramping issues
RCBrooks69
Mar 2017
Atlanta, GA
I'm having some issues with one of our warpers. I'll just put the issue and and see if anyone can help narrow it down for me. As the yarn pulls in from the smaller spools it all collects together on a giant spool called a beam. So that being said, if a string of yarn breaks they must stop the machine to tie it back in before the beam can continue rolling. Once the machine is started back up the ramp up highly overshoots our set point. the set point is 800ypm (yards per minute), but the machine is ramping up to or over 1350ypm causing the yarn to break continually stopping the machine creating a vicious cycle of stopping and starting. Can anyone help with a possible answer as to what I can add or change in the program to decrease the abrupt ramp while keeping the yarn from dragging the ground from a slow ramp?
ramping issue
it passes the set point and works it's way up toward 1350ypm give or take, then it drops down to the set point after the initial startup ramp. it doesn't consistently stay around 1350ypm.
just a guess on my part.
is the ramp up speed set in the drive?
when you start the drive, the internal setting of the drive may be at 1350 and that's where it tries to go.
in the mean time, the plc tells the drive to goto the slower speed.
or
the plc controls the ramp up and the reaction time is too slow and you go to the 1350 speed (approx.) before any speed correction is done.
Like I said, just a guess on my part.
james
I'm feeling more toward the reaction time. I didnt write the ladder, a man before me set it up. I'm trying to figure out how to put a cap on how high the overshoot max is. If I have a set max of 800ypm in the program, there has to be a way I can ramp up without dragging yarn and super overshooting the set point.
What brand of drive/model?
I've worked on a few of those machines but it's been awhile. Doesn't it have a delivery roll that is the master to the beam drive(s)? Then the beam drive is adjusted by a diameter calculator.
it sounds to me like the PID control is running while the motor is stopped
when you do that the PID keeps increasing the speed command until it sees feedback = set point
try this when the motor is stopped set the PID control in manual mode with a manual speed command of 0. that way the PID will calculate the command to the motor as 0 then when it is set back to auto control it will start the command at 0 and work it's way up.
you could also set the upper limit to the command you speed you want and prevent overshoot
This is a West Point warper with a dura pulse drive running Productivity Suite 3000 software. It has a press roll behind the beam operated by hydraulics and pneumatics. I came from the metal forming industry, so this type of plc logic is a bit different from what I am used to.
or
james
An easy way to find out where the problem lies if is in the PLC or the drive. Is to setup a trend, monitor reference speed, start input, and actual drive RPM when you start the machine.
If you note the reference speed ramping up to the SP in the PLC, but the drive actually overshooting then you know for sure something is not setup right in the drive.
If you note the overshoot in the speed reference sent to the drive then you need to tune the PID controller properly in the PLC.
Can you send screenshots or PDF of the logic pertaining to drive signals?
If you have a copy of the Productivity Suite 3000, I could email a copy of the file
PAC 3000 has Word and Bit Histograms.
Word Histogram supports monitoring of 3 numeric tags.
Bit Histogram supports monitoring of 6 binary tags.
You can have both types of histograms running simultaneously - just have a way to indicate start/stop synchronicity.
Consider a textile machine with a first roll pulling material from a supply box. After this first roll there is a dancer roll, that the first roll...
7,083
I have a question concerning the names of the different machines used in the process of turning raw cotton into string/yarn. Amongst the various...
3,576
Good Morning , We have a 100 HP , 480 V (Full Load Amps 124 ) Hammer Mill motor that has a Wye/Delta starting procedure. I would like to put...
4,247
dear all, Please someone help me decode this program: L 5.080000e+002 T #Mandrel_Dia L 7.000000e+001 T...
1,356
HMI design made by me and PLC program made in RSLOGIX 500.
2,613