The Next Stage (1746-HSTP1)

Hello chavak,

Please do not apologies. Okay, I am going to go through it.

Hi, Okay, I have been playing with the wiring from the driver to the ab unit and the CWW & CW works. However, the motor spins the same way....

If I energies CW the motor spins counter clock wise,

If I energies CWW the motor spins counter clock wise,

o_Oo_Oo_Oo_O getting closer
 
Did you try putting back the wiring as original and trigger your CW and CCW jogs. Maybe there was some poor connections in your initial setup.
 
Near as I can tell, the Parker unit you gave the part number for is ONLY step and direction input.

So, your stepper module must be configured for step and direction and I believe that it is not - you must set bit 10 of the configuration word 0 - N7:0 should be changed from -32752 (bits 0, 4 ,& 15) to -31,727 (bits 0, 4, 10, & 15) I order for it to output step and direction as separate outputs to the parker unit.
 

Similar Topics

I've got this start screen where the user has to enter their username and password. The username and password feature works fine. However, I want...
Replies
7
Views
1,443
Anyone know what the little green triangle on SCREEN 3 means ? See picture Thanks
Replies
2
Views
457
What do you guys think of this representation for on/off contacts? C003 is on, then others are off. I have never seen the logic represented in...
Replies
5
Views
1,801
Is it possible to get a report about used digital inputs on GE Proficy? I want to set what inputs are available.
Replies
3
Views
1,085
Hello PLCS.net! Link here: https://www.rockwellautomation.com/en-us/products/software/factorytalk/whats-new.html Seems like Rockwell is actually...
Replies
33
Views
22,425
Back
Top Bottom