Yes, I have the correct bases for the modules.Do you have right terminal module (base) for TC and also for other AI cards?
https://adegis.com/media/asset/1dcad01f3bd0a8e35c4c478c701f3dc6e07263a6471a29699b75a6a82b5dcb46.pdf
Yes, I have the correct bases for the modules.
Reduced the firmware version of the processor from 3.5 to 2.7. Still have the same result.Another one could be that you have selected more recent firmware version for than cards actually has.
Please send a screenshot of the I/O address area of the module's properties. There are a few dropdown menus below the address assignment where you may select which Process Image Partition the cards are associated with.
Have you tried addressing them with %IWnnn?
In the PLC program, create a DB or M tag and MOVE %IWnnnn to that tag.Ok, now how do I access that data outside the process image to for display on the HMI? I cannot create a tag with the address of %IWnnnn.
Thanks.