I have been programing a move instruction of an analog signal into a data block every 30 seconds. For some reason the time works but data is not being moved. Please Help. Is there better way to move data than move instruction?
In this program i used a timer for 30 sec and activate move instruction with timer done bit. When I run the program, it seems like timer done bit never comes true.
Software: Siemens TIA software V12
Thank you.
Put your timer below the Move. Logic is solved from top to bottom.
What am I missing here? I would fully expect dabanani's code to function as he planned it to. This is how I would generate a one-shot every 'x' seconds (and BTW, the positive differential (-|P|-) should not be needed)
The timer's 'done' bit (.Q in this case) should remain on until the timer's rung gets scanned again, which would reset it (IOW, ON for one scan).
Do the newer S7 PLCs have an asynchronous scan?
-Eric
-Eric
From an older post -
- In S7 300/400 plc's the timers update asynchronously to the scan of the program. .......
What's the fastest practical Update Interval you've had success with on the ABCIP driver communicating to L7x series Control Logix? Have an...
636
Hello, I have a issue with tuning a slow acting PID loop using AB PIDE instruction. The system is designed to cool a tank after it heats up...
141
103,113
Hi all, I'm using my 1500 PLC to communicate to two modbus slaves devices via RTU comms: Comms settings being: 9600 8N1 Every now and then the...
2,459
Sir, I want to know time interval function in RS view 32, I want to created one object it's visable after 10 second's. For that I use this...
1,427
How often does Rockwell Release new versions of Studio 5000 Designer? Annually? I'm just curious.
4,442