Timed out reading error in rsviewse
volga
Mar 2007
surat, gujarat
hi all,
i am from india and we have problem from integrating Timed out reading error from 5 slc 5/04 plc. All the data are coming but i doubt that there must be overloaded dh+ traffic. i dont think in our place we can arrange some sort of network analyzer to see network traffic. Due to this our four station running rsview are getting slow down and after few hours we checked there was 34000 error and hmi has gone blank we had to restart data servers.
baud rates is at 57.6 k.
any doubt or tips at station connectors?
Can you remove any of the nodes? try and remove any that you are not using or any that you can stop, then monitor the network and bring them on one at a time
Also is this a new system? or has it been running for sometime, has anyone made any changes??
thanks for ur reply , i will try some issues like overhead time slice setting and cvs bit resettting in plc. also this problem is consistent since many months but as soon as we started trending and alarming whole hmi system got slow down.
also this network is bus topology and our hmi is loaded with many network cnet , dh+ , Serial , DeltaV , and few other. any body know abt some sort of msg/packet counters so that we know status of unack packets.
this is critical problem as pid face plates are taking 30 second to get visible from wireframe. we are underpressure to resolve this issue as our plant operating at 350 KG/Cm2 of hydrogen pressure.
please help
volga said:
...but as soon as we started trending and alarming whole hmi system got slow down.
Check your sampling times on your trends, if you have these set very low (several times a second) then it will use take up a lot of space on the network, you could also look into changing the baud rate from 57 to 215? (forgot what the higher speed is)
But I would look into the sampling times first, some of your trends you may be able to slow down to several times per minute verses several times per second
Good afternoon all I'm a bit puzzled. 19 inch AB HMI. addressed 192.168.1.22. laptop 192.168.1.10. I can see it in Linx. I can download .mer to...
637
Hello All! First Post! What is the "Timed Out" Check Box used for on the MSG instruction in Logix5000? This check box is located under the...
1,887
Today when an operator went to start a piece of equipment that gets infrequent use they got a bunch of time out errors. Multiple errors saying...
5,654
Hello, I've done several migrations from SLC 5/05's to 5370 L33ER Compactlogix controllers. I've just encountered my first PID instructions with...
1,709
On one of our conveyors we have a height verification sensor that is triggered by a photo eye as product passes by. QA wants another sensor to...
2,320