Timer Display: AD D0-06/C-More EA9
Jeff164
Mar 2017
NJ
Hello
I'm still fairly new at PLC work, as my job requires much more than just PLC code, so I cant devote all my time to it, so please bear with me.
I have an application where the end customer will enter a desired time setpoint on a setup screen, generally 10 to 60 minutes. This timer will be triggered at the end of a process pumping cycle. When the main motor shuts off it triggers a change in pointer state that is on the enable rung of a TMRA timer. When the referenced timer times out, the system will change state again to its final idle state; where it waits for operator input to start another cycle.
I have it all written and functional, however I have issues with the display.
There is a status screen that will give a countdown value of this TMRA function and the display is being erratic. The numbers start fairly close, then actually increase in value before settling down and counting down to zero when the TMRA times out. When TMRA times out it resets itself and also drives another change in pointer state so that it will not be re-energized again until another run cycle is triggered and subsequently completed.
Here's the logic I am using:
I am using a 32 bit BCD input tag to a V1364 v-memory location to bring the user provided value. The C-More is scaling the value from minutes to tenths of a second for the TMRA preset.
The TMRA timer is reset by a rising pulse of its own output coil, or by the pump starting back up (if the user requests an immediate run).
The output countdown display of the TMRA function is obtained by taking the TMRA Preset and using the LDD function to load to the accumulator, SUBD subtracting the timer accumulated value; and then OUTD to write the result as a 32 bit BCD to a new Vmemory location, which I assigned to V1366.
Then the C-More takes V1366 and does another scaling back from the 32 bit BCD value in tenths of a second to minutes.
Like I said - it sorta works .... but if you watch the display carefully - its erratic.
If helpful I could maybe post screenshots of some of the relevant code.
suggestions ? and Thank You !
Jeff
Thanks Garry, I had called AD's tech support and the guy I got alluded to the fact that he doesn't like using timers- and suggested using counters, and initially it seemed complicated but now that I think about it....maybe much simpler.
I'll post back and let you know how it goes.
Thanks to both Bernie and Garry. I had indeed checked the data types, was using the 32 bit BCD for the double V memory allocation on both the data entry and reading the output values. (Number type mismatch was my last snafu on the last project).
At any rate; Garry's suggestion was easy enough to implement and has corrected the matter.
I thank you for your assistance.
Needing a panel mount style timer that would interface with a large numerical display. Tankline with 20000 + gallon dip tanks. Operators lower...
1,920
Can someone tell me how to display a timer value when creating a screen in Factorytalk View ME?
4,133
I have a TON timer (60 sec) I want to display the timer on the panel view, but when I set the tag, there is no data type for time... How can I...
2,571
Need help a value to display properly on a PanelView 300. I can get it to display but counting in minutes decresing from preset value of TON ans I...
4,374
Hi, I am using micrologix1500 and Panel View C600, 1)I want to display timer value in HMI c600, so How can I do it. 2)I want to display...
1,640