OK, you are not on as new a version as I had guessed.
These are all newly created applications, yes?
You are not converting from PanelBuilder32 to Factory Talk View ME?
While I await that confirmation I'll start giving you something to try...
See here...
35211 - FactoryTalk View ME: Error - Unable to Save Application Information
Access Level: TechConnect
...specifically Solution 2 - Repair FactoryTalk Services Platform
It is often the case that the FactoryTalk Directory (FTD) is corrupted within FactoryTalk Services Platform (FTSP).
If you do not have a TechConnect Contract to view that article then here is the procedure...
To perform a repair do the following:
Close all Rockwell software products...
Windows XP:
Go to Start>Control Panel>Add or Remove Programs...
Highlight "FactoryTalk Services Platform"...
Select Change>Next>Repair>Next>Install...
Windows 7:
Go to Start>Control Panel>Programs and Features...
Highlight "FactoryTalk Services Platform"...
Select Repair at the top of the window...
You should then be prompted to reboot the computer.
Try that and see how you go?
Regards,
George