having trouble getting slc5/03 allen-bradley to communicate with pc.
tried auto configuration
please help
thanks
The "phone jack" port requires a 1747-PIC converter. The DB9 port requires a "cross-over" or "null modem" cable (AB part number 1747-CP3). Which port are you trying to use? Quick tip: if you're using the DB9 port and the DF1 driver won't work - try using the PIC driver in RSLinx - even though you're NOT using a PIC converter on this port. Yes, I know it sounds dumb - but try it anyway. You might get lucky.
PCMK
If you by chance have a pcmk card and cable #1784-pcm4/b, you can use this combination. Just remember to change network type in driver config. to dh485.
Thanks for the reply's
I am using RS232 cable/ it is a homemade cable inwich
pin 2&3 cross
pin 5 straight across
pin 4-6 &1 tie
pin 7&8cross
but the only light on the plc that will flash is the DH485
by the way I am using rslinx lite
The SLC 5/03, SLC 5/04, and SLC 5/05 processors can communicate by
means of the RS-232 communication port, channel 0. Channel 0
supports DF1 full-duplex protocol and DF1 half-duplex master and
slave protocol, DH485 protocol, as well as ASCII communications.
Refer to your programming software user manual for information on
configuring the RS-232 communication port, channel 0.
The details of the DF1 protocols can be found in the DF1 Protocol and
Command Set Reference Manual, Publication Number 1770-6.5.16.
Channel 0 provides a minimum of 500V dc isolation between the I/O
signals and the logic ground of the SLC 5/03, SLC 5/04, and SLC 5/05
processors. The channel is a 9-pin D-shell. The table below provides
a description of each of the pins.
The D-shell is the bottom port on the SLC 5/03, SLC 5/04, and SLC
5/05 processors.
Pin Pin Name
1 DCD (Data Carrier Detect)
*2 RXD (Receive Data)
*3 TXD (Transmit Data)
4 DTR (Data Terminal Ready)
*5 COM (Common Return [Signal Ground])
6 DSR (Data Set Ready)
7 RTS (Request to Send)
8 CTS (Clear to Send)
9 NC (No Connection)
Look at Appendix B of this manual:http://www.ab.com/manuals/cp/1747-um011c-en-p.pdf
When you goto "autoconfigure" make sure the type of connection is selected to SLC (its the top right hand window) the default is PLC. This caught me out a while ago.
Title summarizes the overview of the problem. I am trying to make AVEVA Edge 2020 and a Schneider TM241CE40R to talk to each other via Modbus...
18
2,101
Need You help... Trying to setup an communication between two PLC's [1756 L61 & 1756 L72 ] thru ethernet EN2T. first i added the EN2T module in...
1,934
Does anyone have experience communicating with the MAGPOWR Cygus Tension Controller thru Ethernet. I have a Controllogix 1756-L73 PLC Version 30...
25
4,082
I am still learning this PLC stuff, so yeah this is what I got. PLC's I am swapping: 1)On the side FX3U-80MT/ES, On the front 80MT/ES 2)On the...
2,643
Hi all, Got a new device I'm trying to work out how to communicate with. It came along on Monday morning after 9 months of development inside my...
19
5,747