Longbow Member L Join Date Dec 2005 Location Bavaria Posts 19 Jun 9, 2010 #31 mer said: http://www.automation.siemens.com/m...0/function-modules/FM352-5/Pages/Default.aspx Click to expand... This is the SIEMENS Boolean Processor: No analog In- or Output! Reduced instructionset, no realtimedebug. No onlinechange!
mer said: http://www.automation.siemens.com/m...0/function-modules/FM352-5/Pages/Default.aspx Click to expand... This is the SIEMENS Boolean Processor: No analog In- or Output! Reduced instructionset, no realtimedebug. No onlinechange!
MichaelG Member M Join Date Nov 2006 Location Brisbane Posts 691 Jun 9, 2010 #32 Update on whirlair's Control logix card It's the Fast analog input 1756 - IF4FXOF2F/B Samples at 0.3 of a ms AND sends the PLC up to 20 samples at at time Must use the archiving connection when adding the IO. 1756-td002_-en-e.pdf Michael
Update on whirlair's Control logix card It's the Fast analog input 1756 - IF4FXOF2F/B Samples at 0.3 of a ms AND sends the PLC up to 20 samples at at time Must use the archiving connection when adding the IO. 1756-td002_-en-e.pdf Michael