Unity Pro XL assembly instance reading problem
oxykill
Jan 2013
Quebec
Hi there everyone,
I`m currently working on a Toshiba drive with ASD-G9ETH communication card on it, this drive is linked on our network.
So, i`m able to read one by one register (and write also), but i need to retreive command and status word.
In the provided documentation the always talk about assembly instance, it show an exemple with RSLogix, but I can`t understand how to make it work with my unity program
http://www.toshiba.com/ind/data/tag_files/Ethernet Card ASD-G9ETH Manual_3916.pdf
Page 71 - 72
Thanks for helping :)
I had a look at the user manual and I couldn't find page 71-72, and searching for 'assembly' in this document gave me no hits...
Is this the correct manual? The manual you provided shows only support for explicit messaging, either UCMM or Class 3 (connected), and the use of assembly instances is best reserved for Class 1 or I/O communications. I can describe ways to get data through EtherNet/IP with the given user manual (actually - I would suggest moving to ModbusTCP in this case because as far as I can tell, from Rockwell's data access guide, the data_table_read service is vendor specific) but since you mention assembly instances you are hopefully using Class 1 communications, which is MUCH easier and can be preferable to ModbusTCP if available and is more general so not vendor specific.
Which platform are you on: M340, Premium, or Quantum, and which Ethernet device do you have?
Sorry, wrong document :
http://www.toshiba.com/ind/data/tag_files/ASD-G9ETH_Operation_Manual_4749.pdf
I finally found my problem, i'm not able to use assembly, so I communicate with the device with command word (parameter 1007 - 1008).
I'm on TSX premium PLC, just needed to configure I/O scanning on my drive ip adress, then write 1007 - 1008 register and it's work !
Thread Close, everything working fine :)
If you had a TSX ETC 101 Ethernet module for the Premium platform then you could use EtherNet/IP and the Class 1 communications that are listed in this user manual. I assume you went ModbusTCP with IOScanner... and it works... so all is good.
This module would do both EtherNet/IP and ModbusTCP with IOScanner so is dual-protocol capable. However, the other ones (embedded port or ETY family) are ModbusTCP only, so I suspect you have one of those.
Hello, I am using Unity pro V15. I have Quantum CPU 671 and Ethernet NOE 77101 configured. I have configured IO scanning on NOE. I have attached...
179
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
404
Hi All, I haven't installed Unity Pro in years and needed to install it recently. I initially tried installing Version 11.1 and the whole...
716
Hello i want to implement a Read_var / Write_var functions to communicate with a modbus tcp device at the moment i use the unity simulator at the...
1,929
Hi, I've exported a PL7 application to the .FEF file succesfully. Imported the .FEF file in my Unity Pro project, but two of the five sections in...
775