unstable analog input
harrydeharry
May 2008
Delhi
237
Dearall,
I am using a Delta SS2 PLC with 6xa analog card,
[ TO K0 K1 H480 K1]
using first two analog inputs ans 0~10 v dc input and rest of the two as
4~20 ma, if I check my input from the device in a form of 4~20 its coming stable, while checking on plc it is very unstable, while i have checked it with shelled cable, groundings, other noises etc.
Please suggest what cud go wrong as i had not used delta as well as analog much.
BR
Well the shield should only be. connected at 1 end so the interference drains instead of causing a ground loop. secondly it is possible your meter isn't fast enough to.detect the changes the Plc is seeing. you can make averaging logic to smooth the signals out.
Common mode voltage
Harry,
What is the common mode voltage between the channels? Most analog input cards can deal with 5 vdc between the channels, but any large difference will cause problems.
Steve
1762-IF2OF2 Analog Input Problem I use Micrologix1100 and explantion 1762-IF4 and...
2,606
i have a GE fanuc 23 point versa max with 2 inbuilt analogue inputs, the problem i am facing is an unstable reading, i am using a 4-20 mA danfoss...
4,257
I have done a lot of SLC and Micro work put have not ventured into the Compact world till now. I have an engineering firm I work with that has a...
2,376
It takes a minute or two just to open, I think this is from the license checks. After it is open it takes like 5-10 minutes to upload a 2.5MB...
1,211
Hello all! I am trying to figure out how to tune PIDE for an unstable heater. This is a startup tuning. My project was to remove old temp...
3,261