Upgrading from 1756-L61 to 1756-L71
aleon
Jan 2022
Lorain, Ohio
Hi All,
I'm trying to upgrade from 1756-L61 to 1756-L71 but I keep getting an error 25299-0. Is there anything that need to be complete to be able to upgrade?
Hi All,
you pretty much need to change the processor type manually in an .l5k filetype.
you can do that by saving the current project as .l5k
create a new project with the processor type you want to switch it to. then save that new project as .l5k, and then copy/paste the 'Processortype' 'CatalogNumber' and 'ProductCode' from the new project, to the old projects ascii text file (l5k).
then try to reopen the old project that you wanted to change.
I've done exactly this upgrade (L61 to L71) and did this step with the .L5K files and it worked perfectly. Just open the .L5K up in Notepad (or any other text editor) and swap out those fields for the new ones.
Welcome to the PLCTalk forum community !
Are you changing the controller type but leaving the firmware major revision the same ?
What exact version of RSLogix 5000 / Studio 5000 Logix Designer are you using ? The minor revision might matter.
Is there any other text in the error message ? Where and when, exactly, does it show up ?
I agree that changing the controller type in the L5K format might be the easiest way to circumvent a controller type change error.
I have to Flash upgrade an existing L61 controller on V15 to at least V17. a. Because I have used Add-On instructions in the new code (>= V16)...
2,421
Hi, I am upgrading a Wonderware SCADA form version 9.5 to version 23. I am able to migrate all the graphic, but when to activate the runtime this...
420
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
551
I am looking to upgrade some of our old Servo Drives to the newer kinetix 5700 style. currently we have 4 1394 axis that are all driven by 5kw...
886
Hello, We are currently running a bunch of g310's connected to their SLC5 PLCs through ethernet. I've attempted to upgrade the program from 2.0...
1,126