UPS Recommendations. Online or not.

Cwill

Member
Join Date
Jan 2017
Location
Vancouver Island
Posts
8
Our remote location often sees power outages. The site has a standby generator that comes online about 20 seconds after a utility power failure but this forces the our Horner XL4 PLC to restart. We would like to have the PLC on a UPS that would give us a runtime of 5 to 10 minutes. This would bridge the power gap and allow the PLC time to notify the operator if the generator does not come online and then gracefully shut it self down. We have been quoted for an online 120VAC UPS that would give us a run time of several hours but this seems like expensive overkill.

Does anyone have any recommendations for rail mounted UPSs? Is an online UPS recommended or necessary? TIA
 
I have used the Allen Bradly 1609-B series of UPS in control panels and have had good luck with them. I think they come in 350W and 500W. Normally more than enough power for a PLC.
 
Online in the UPS world means that the power for the system is provided by the UPS even when there is proper input power to run. So when you lose input power the system just keeps on supplying output power until the battery is dead. The transition is seamless.

If the UPS wasn't Online it would have some kind of switching system that would sense the loss of power and then "Kick in". That isn't the way you would normally want to run a Control System. The "bump" from the changeover could cause lots of issues. I doubt that you will find an Industrial UPS that isn't Online.
 
The term UPS intones AC power and shouldn't be used (IMHO) unless there is an inverter involved. The phoenix device is what you want. Or you could use a battery charger and connect the PLC to the battery which is what we normally do. Sure the PLC sees 27.2V and will get browned out if you let the batteries go flat but so far that hasn't caused us any problems.

what is your industry?
 
The present power supply is a Siemens LOGO!Power 24 V @1.3 A DC. PLC draws 190 mA @ 12 VDC

Do I know what the actual draw is? No.

That should be good enough for sizing, say 1.3 amps...it would be a different story if you had a 20 amp power supply and didn't know what the actual draw is, I mean you have i/o that requires 24VDC, solenoids, relays, etc.
 
Hi Cwill.

We use an online UPS purely to keep critical equipment powered during a dip such as the PLC, HMI any critical solenoids etc. Our usual setup is so the UPS will power the 24VDC power supplies in the panel and thus the PLC & HMI etc. We then monitor the state of the incoming 3ph and if there is a dip then we pause or stop process that will be affected or take other necessary steps.


We use an online UPS (usually a 1kVA unit), rather than a line-interactive UPS, as the load is continuously supplied by the battery pack via the inverter so there is no dip in the output when the main power drops, a line-interactive UPS will have a few milliseconds dip.
The online UPS also provides better noise/surge suppression as well as a true sine wave rather than a simulated sine wave.
I have not had an opportunity to use the DC style UPS units, as they are generally rather expensive here, so I cannot comment on them.

Cheers
Guy
 

Similar Topics

I've got a new and different project and I need a DIN mount UPS with 120V output. SOLA comes to mind but are there any other options you folks...
Replies
10
Views
1,141
Hi guys, its my first time progamming cicode and I need to do popups alarms, there are several digital alarms and in their rising edge transition...
Replies
0
Views
512
This is a very basic question regarding whenever I close any Display, Library etc. It asks me to save changes all the time even without any edits...
Replies
4
Views
844
Looking for a UPS that integrates well into a L8xE Control logix installation. We have used the AB 1609-D1500N Ethernet IP UPS's in the past, but...
Replies
7
Views
1,936
Hello Everyone, I hope all my American friends had lots of Turkey and Football! What is everyone using for UPS power for Panel PCs? I am...
Replies
2
Views
903
Back
Top Bottom