Prayder Lifetime Supporting Member P Join Date Jun 2014 Location Arkansas Posts 254 Apr 14, 2015 #1 I am using an RTO to log the amount of time a button has been pushed. I was wondering when I add it to the rung how do I set the preset? It wont let me click on it like a ctu will.
I am using an RTO to log the amount of time a button has been pushed. I was wondering when I add it to the rung how do I set the preset? It wont let me click on it like a ctu will.
PLCnovice61 Member P Join Date Apr 2015 Location home Posts 377 Apr 14, 2015 #2 try off line and download
MarkNightingale Lifetime Supporting Member + Moderator M Join Date Sep 2010 Location In The VAT Shed Posts 744 Apr 14, 2015 #3 It will only let you select the preset after you have defined the new tag as a timer. Cheers Mark
Prayder Lifetime Supporting Member OP P Join Date Jun 2014 Location Arkansas Posts 254 Apr 14, 2015 #4 sorry but not sure what you mean when you say "defined the new tag as a timer". I created an RTO and chose the T4[36].ACC as the timer...
sorry but not sure what you mean when you say "defined the new tag as a timer". I created an RTO and chose the T4[36].ACC as the timer...
gravedigger02 Member G Join Date Jan 2008 Location New Brunswick Posts 47 Apr 14, 2015 #5 You have to be in edit mode to change the preset.
Prayder Lifetime Supporting Member OP P Join Date Jun 2014 Location Arkansas Posts 254 Apr 14, 2015 #6 I already am..
PLCnovice61 Member P Join Date Apr 2015 Location home Posts 377 Apr 14, 2015 #7 if everyone posted the problem code, at the same time the question was asked the answer would be much quicker!!!
if everyone posted the problem code, at the same time the question was asked the answer would be much quicker!!!
gravedigger02 Member G Join Date Jan 2008 Location New Brunswick Posts 47 Apr 14, 2015 #8 Are you using PLC5 or SLC500
Prayder Lifetime Supporting Member OP P Join Date Jun 2014 Location Arkansas Posts 254 Apr 14, 2015 #9 Studio 5000 with ControlLogix 1756-L71 processor
gravedigger02 Member G Join Date Jan 2008 Location New Brunswick Posts 47 Apr 14, 2015 #10 Can you post the rung in question
PLCnovice61 Member P Join Date Apr 2015 Location home Posts 377 Apr 14, 2015 #11 lets drag it out, please post it so you can help yourself
MarkNightingale Lifetime Supporting Member + Moderator M Join Date Sep 2010 Location In The VAT Shed Posts 744 Apr 14, 2015 #12 This looks like a conversion from an SLC to a control/compact logix. Why are you entering the .acc as your timer? You only need to have T4[36] as the timer. Cheers Mark
This looks like a conversion from an SLC to a control/compact logix. Why are you entering the .acc as your timer? You only need to have T4[36] as the timer. Cheers Mark
Prayder Lifetime Supporting Member OP P Join Date Jun 2014 Location Arkansas Posts 254 Apr 14, 2015 #13 that's what it was.... I dont know why I had chosen t4[36].acc... when i changed it to just t4[36] it worked.. thx guys.
that's what it was.... I dont know why I had chosen t4[36].acc... when i changed it to just t4[36] it worked.. thx guys.