using l36erms when safety isn't needed

Join Date
Aug 2021
Location
tecumseh mi
Posts
52
Howdy everyone,
I have a project that i am duplicating on an older version of the same cell. With all the additional stuff that has been added the 1769-l30er memory isn't enough, i am about 80kb over the 1mb capacity. The cell i am duplicating has a L33er in it which I have a quote for, but we have a couple extra l36erms from a different project that got upgraded. I don't need the motion or the safety, I just need the capacity. Other than the additional power it pulls, are there any concerns with using this one? Anything I would have to do on the safety side because it does have a safety side?
 
Empty Safety routines do nothing and have no effect on normal logic. Other that being a little overkill the L36ERMS should work just fine.
 
I have seen safety faults in processors with empty safety routines. To attempt to prevent that, I always have at least have one rung of logic in the safety routine. Usually that is a rung that unlatches a tag "Always Off".
 

Similar Topics

I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
64
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
124
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
222
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
60
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
109
Back
Top Bottom