I am working on a Controllogix project with redundant PLCs. The primary and secondary racks both contain:
[0]L71
[1]EN2T
[2]CN2R
[3]CN2R
[4]RM2
Each of the two CN2R modules are accessing different remote CN2R modules connected to Remote IO. Say slot [2] is connected to side 1, and slot [3] is connected to side 2. Both CN2R modules are on the same network. The way it is set up right now is if slot [3] gets disconnected in Chassis A, the system will switch to Chassis B. If slot [3] also gets disconnected in Chassis B then I lose connection to all IO on side 2. Is there a way to maintain this connection through slot [2]?
Thanks in advance!
I think if Chassis A, Slot{3} connection failed, AND Chassis B, Slot[3] failed, both of them using redundant media, then you've had four failures....
I would be looking elsewhere for a solution, rather than trying to hold onto a connection that has already failed four times.
But a simple answer is :- yes you might be able to schedule all your I/O in both CN2Rs, and programmatically inhibit the connections served by the other module. But if that were plausible, why were 2 CN2Rs used in each chassis in the first place ?
Good Evening , How easy is it to setup and communicate with a AB MicroLogix with a C-More EA-3 HMI ( Serial ) ? Thanks for your help and...
1,543
Dear all I want to make S7-1200 as Modbus RTU gateway (Master and slave all in one) I have bought : 1 x 1214C CPU 2 x CM1241 RS422/485 The fisrt...
4,075
I am trying to setup a TCP/IP connection from a PC to a Do-More PLC. I have the PLC set up as the server and am getting data into the buffer...
2,143
Hello everybody, I am developing an application with CLogix that involves a lot of discrete I/O such as selector switches, pushbuttons...
8,454
Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
28