Using Rslogix500 in lieu of DAT unit?

RyeGuy

Member
Join Date
Sep 2019
Location
Toronto
Posts
11
Hello,

Is it possible to use the RS logix 500 software to mimic any type of commands that the 1764-DAT unit on the ML1500 plc uses?

I have a Password protected software but the DAT tool can be used to access some critical information for troubleshooting/resetting the software program.

Any help or other work around without the obsolete 1764-DAT would be helpful !
 
RSLogix 500 would need to "go online" with the controller before it will give you data table access, and that requires a password.

RSLinx Classic has a read-only "Data Monitor", though I don't recall for sure if you need a DDE/OPC capable license or if RSLinx Lite supports that features.

And of course any HMI will let you access the data table unless they're read or write protected.

RSL_Data_Monitor.PNG
 

Similar Topics

Hello Guys, First off Happy Holidays! (edit: I am using Rslogix5000 not 500. sorry!) I am a beginner programmer trying to sort out some code...
Replies
1
Views
1,597
On our RsLogix500 software I would like to know how I can compair two programs for trouble shooting programs for same machine usng the compair...
Replies
5
Views
1,569
Hey all... this is a bit of a long one so bear with me... Is there a way to use a bit from Rslogix500 that is on a SLC in a Rslogix5000 program...
Replies
12
Views
9,781
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
64
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
124
Back
Top Bottom