vanishing trend

unsaint32

Member
Join Date
Oct 2012
Location
minneapolis
Posts
365
With Controllogix (V20 & V21), when I trend, if I set the time to more than 3 minutes, the trend lines disappear. Is there a way to prevent this? I am attaching a screenshot of this issue.

vanishing trend.jpg
 
Right-click on the Chart (onscreen or in the Project Organizer) to go to Chart Properties, then select the Sampling tab.

There's a section where you can select the trend's limit on the number of data points.

You can select an absolute number of samples, or a time period, or just choose to fill up your hard drive.

That's probably what's going on; four Pens at 3 ms sample rate would accumulate 1333 records per second, so it would exceed the default 200,000 record limit in 2 1/2 minutes.
 
Right-click on the Chart (onscreen or in the Project Organizer) to go to Chart Properties, then select the Sampling tab.

There's a section where you can select the trend's limit on the number of data points.

You can select an absolute number of samples, or a time period, or just choose to fill up your hard drive.

That's probably what's going on; four Pens at 3 ms sample rate would accumulate 1333 records per second, so it would exceed the default 200,000 record limit in 2 1/2 minutes.


I selected no limit but the vanishing trend issue is still happening as you can see in the picture I am attaching.

vanishing trend-2.jpg
 
At 10 ms sample time, you appear to get a six minute trend,
which is probably still faster than your scan time,
give 100 ms a try, its still fairly fast out in real world time
 
Instead of attempting to poll individual data points extremely fast, RSLogix 5000 and the ControlLogix controller use some controller memory to store the data fast and upload it to the TrendX object in big chunks.

It's possible that you're running into a limitation of this function that isn't obvious in the configuration screens.
 
On a related note, if your trend sample period is faster than your task scan time, is the trend data still valid? Or are they even related at all? I have a 15mSec scan time for my task (the entire processor logic is in the single continuous task) and I have trend sample period at 1mSec. The trend *seems* to be showing tag data changing at a rate even faster than the scan time, but I wanted to see if the data was actually valid.
 

Similar Topics

So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
60
Hello, We recently upgraded our control server to a newer model. After the transition we are experiencing issues with our trend graphs to where...
Replies
2
Views
125
Our punch press has a SLC500 with HELM weight module (HM-604-WM) for tonnage monitoring. The operator enters the weight range on the HMI, which is...
Replies
9
Views
207
Hello. I am working in FTVSE v8. I have many trends set up some of them work others do not. The ones that don't work show the foot print of the...
Replies
3
Views
242
Hello. I am rebuilding an HMI from 2003 with the new software Factory Talk Optix. I have a pop up box with a trendline on it. I want the ability...