I just finished analyzing some blower test results. This uses a high-speed permanent magnet synchronous motor (25,000 rpm) controlled by a VFD at 417 Hz. The Amp draw on the line side of the VFD measured with a quality power analyzer was 412 A. The VFD display showed the current on the load side of the VFD as 460 A. The VFD display showed a power output of 300 kW (400 hp). Assuming a 95% efficiency the motor shaft hp would be ≈ 380 hp. The test load exceeded the actual field load, and the projected field hp draw would be 8% lower, ≈ 380 A and ≈ 350 hp.
I've never looked at this data before, and it raises two questions.
1) Why is the current to the motor higher than the current into the VFD?
2) Should the conductors and branch circuit protection to the package be based on 412 A or on 380 hp or 350 hp?
I've never looked at this data before, and it raises two questions.
1) Why is the current to the motor higher than the current into the VFD?
2) Should the conductors and branch circuit protection to the package be based on 412 A or on 380 hp or 350 hp?