VFD Amp anomalies

Tom Jenkins

Lifetime Supporting Member
Join Date
Apr 2002
Location
Milwaukee, WI
Posts
6,302
I just finished analyzing some blower test results. This uses a high-speed permanent magnet synchronous motor (25,000 rpm) controlled by a VFD at 417 Hz. The Amp draw on the line side of the VFD measured with a quality power analyzer was 412 A. The VFD display showed the current on the load side of the VFD as 460 A. The VFD display showed a power output of 300 kW (400 hp). Assuming a 95% efficiency the motor shaft hp would be ≈ 380 hp. The test load exceeded the actual field load, and the projected field hp draw would be 8% lower, ≈ 380 A and ≈ 350 hp.

I've never looked at this data before, and it raises two questions.

1) Why is the current to the motor higher than the current into the VFD?

2) Should the conductors and branch circuit protection to the package be based on 412 A or on 380 hp or 350 hp?
 
Last edited:
Tom that happened to me several years ago with allen bradley equipment, I was supposed to use that data to charge Kwh, I asked AB people the reason why and they told me that they had problems with hall effect sensors. Since then I never use drives to measure current and voltage. Maybe other brands don´t have this problem.
 
I just finished analyzing some blower test results. This uses a high-speed permanent magnet synchronous motor (25,000 rpm) controlled by a VFD at 417 Hz. The Amp draw on the line side of the VFD measured with a quality power analyzer was 412 A. The VFD display showed the current on the load side of the VFD as 460 A. The VFD display showed a power output of 300 kW (400 hp). Assuming a 95% efficiency the motor shaft hp would be ≈ 380 hp. The test load exceeded the actual field load, and the projected field hp draw would be 8% lower, ≈ 380 A and ≈ 350 hp.

I've never looked at this data before, and it raises two questions.

1) Why is the current to the motor higher than the current into the VFD?

2) Should the conductors and branch circuit protection to the package be based on 412 A or on 380 hp or 350 hp?

Current on the motor side includes the reactive current, i.e. the motor's actual Power Factor. Current on the line side is at a relatively consistent .95 PF because of the DC bus capacitors.

Line side conductors are to be sized at 125% of the rated INPUT current of the VFD, per 430.122, partly for this reason, but also because some Asian drive mfrs base their larger drives on kW rated motors, so they end up over sized for HP rated motors and the rated input current is actually higher.
 
On the load side, you are measuring the apparent intensity, which is the vector sum of the active and reactive currents, and therefore greater than the active one, which is the one that really does work.

I thing that the cables on the load side should be sized for the apparent current, that is, for 460A x 1.25 margin = 575A

On the line side, with a 25% margin they would have to be rated for about 500A
 
It also depends on the output voltage to the motor. If the Input is 460v, and the output is 400v for example, then the output current can be 15% higher... This always throws my customers off when they are running below base speed :D
 

Similar Topics

I am trying to find the operating limit range of a few conveyors. In the event one of them breaks I want to see the abnormal value and use this...
Replies
11
Views
1,341
i have a motor (3.7kw ) which draws current around 5amps when running on DOL, same motor when running with vfd on max speed draws 12.5 amp...
Replies
6
Views
3,433
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
40
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
170
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
152
Back
Top Bottom