Hello,
We need to communicate Mitsubishi vfd (E700 Series) of around 32no's over a long distance around 2000meter from Mitsubishi PLC control room. individual distance between vfd's is around 400meters and nearest Vfd from control room is at around 1200 meter. Which Network Architecture and Protocol needs to be used.Plz share your experiences. Thanks
thanks all for reply
I want to know what is the maximum distance between two station (between two vfd's) and master plc. Not found any satisfactory answer in manual. Because in this case distance between two vfd is around 400-500 meters. Will CC-link network work with this much vfd to vfd distances ??
I know the B&B units will work at much greater distances. They have direct RS 485 ports. No adapters need once they are set up they work good. Give then a call that will help you
Only if you had 2 or 3 VFD's maximum.
It's in the manual I posted earlier. Page 29. Link.
If you run at the slowest speed, the maximum length of your entire network is 1200 meters. It won't work without repeaters, or fiber adapters.
Use the B&B I set one u years ago if I remember we had about 30 vfd's on the network with 1 master
use them as a wire replacement for an RS485 network
range of about 20 miles should do everything you want easy setup with great tech support
Hello, We have several Yaskawa GA800's installed in our plant. They are all controlled via Ethernet and they work fine. However, they all get...
482
Hi, Does anyone do a communication of Ansaldo VFD to a PLC? what i saw on the display setting of Ansaldo VFD is that the baudrate is 187k. I...
1,501
Hi everyone, I would like to use Micro 850 to control DF FC 102. I adready connect Danfoss fc 102 VFD ( it can run the motor) to Micro 850 by...
1,936
HELLO EVERY ONE I need help in i am trying to establish modbus communication between two vfd's and delta plc the problem is that only one vfd is...
1,735
Hello Everyone I am trying to establish RS485 communication between Mitsubishi vfd E700 and delta plc DVP20EX00R2 The problem i am facing...
2,477