VFD Motor Parameter Auto-Identification
Jieve
Feb 2012
USA
274
Hey guys,
I was wondering if anyone could shed some light on what actually happens during the stationary and rotational motor parameter auto-identification that takes place when commissioning drives. The Siemens G120 units I've been working with apply something like 20V on and off to the motor (1hp, 400V) in stationary mode, then run it at around 1500 rpm for around 30 secs with 3-4 quick accelerations in the rotational ID mode. What parameters specifically is the drive measuring during each of these processes?
I believe that in sensorless vector mode, the drive does both the stationary measurements and the rotational measurements when I select them both, but if I remember correctly, I thought in V/hz mode it only did the static measurement. Does this make sense?
Finally, should the motor always be decoupled from the load during this process? Or connected to it (assuming no damage can be done)?
Thanks!
The purpose of the motor ID run is to allow the VFD to create a motor model in its memory that it can consult for % of nameplate torque and motor shaft speed. To determine shaft speed, a good motor model will need to know exactly how much slip occurs for each ft-lb or torque in the shaft, the motor rotor inertia, as well as correct motor nameplate data. Without this model, the VFD sensorless vector performance would be worse than if you had left it in V/hz mode
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
149
HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
670
Hello all, Quick question. If motor name plate says 1400 RPM @50 Hz and VFD speed is set to 20Hz does that mean the motor shaft is rotating at...
805
Hi, The distance between a Yaskawa VFD GA700, 45KW and the motor is 75 meters. I am using an output inductor between the VFD and the motor. I...
946
Is there any issue with running a VFD-controlled 3-phase induction motor in torque control mode in the braking region continuously (back-driven by...
4,038