VFD SLS with no encoder

rQx

Lifetime Supporting Member
Join Date
Oct 2010
Location
Trelleborg
Posts
1,051
Hi,
Is there a VFD that can do SLS without an encoder to ANY motor. I know siemens has it but you have to have a special motor from them.
/Tim
 
It's not something I've used, but my G120 course notes say that SLS does not require encoder feedback on the G120. Requires a CU240E-2 F or a CU250S-2 control unit. Will probably also require start drive advanced, safety advanced and it mentions that each axis requires a licence but unsure which specific licence it means.

The only mention of specific motors is this:
"Encoder-less operation is possible for all asynchronous motors and the synchronous motors 1FU8 (SIEMOSYN)"

I looked up 1FU8 and they're all synchronous motors, so I'd take that to mean any asynchronous motor can be used but only that specific synchronous motor.

Siemens also says that the G130 and G150 have the SLS function.
 
I read "The use of this safety function without encoder is permitted for asynchronous (induction) motors or synchronous motors of the SIMOTICS A-1FU series (previously: SIEMOSYN)"

https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/10290371

May be worth asking Siemens technical support about this wording if it fits the bill for your project.

IÂ’m reading that as:
-Any asynchronous motor
-Synchronous motors of the 1FU series

But it could well be
-asynchronous motors of the 1FU series
-synchronous motors of the 1FU series

But a quick google only returns results of synchronous motors.
 

Similar Topics

I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
71
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
182
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
166
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
307
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
13
Views
479
Back
Top Bottom