vfd triggering inputs
bbseay
May 2003
OK.
54
Whenever my vfd kicks in it makes a few inputs come on and fault out my program. I am using everything AD. vfd is not in the plc panel, but inputs, outputs, and vfd outs are in the same conduit going to the machne 40 feet away. where in the system could the interference be coming from?
TIA
Billy Seay
bbseay, keeping this as simple as possible, the leads from the output of the vfd to the motor are terribly noisy. They must be separated from all other wires including power wires ideally.
That's by far the most likely source of your problem.
bbseay,
Let us clear up the confusion. When you said "inputs, outputs, and vfd outs", I think we mostly understood that by inputs and outputs you meant the PLC I/O, but exaclty what did you mean by "vfd outs"? Are you referring to the PLC outputs that control (start/stop, change speed) the Variable Frequency Drive?
As was stated, move your motor leads or screen them from any other wiring. VFD motor outputs creates harmonics which in turn is noise (voltage) induced into other wires and can create false signals.
It appears that there might be an "assumption" happening here...
Has this drive ever worked correctly?
Is the program "known" to be good?
Are you using "outputs" from the drive to send "input" signals to the PLC?
If so, what are those "outputs"? What "signals" do they provide?
Are these programmable outputs? Are they configured properly?
Could the problem be something as simple as looking for the "Running" signal as soon as the "Run" signal is sent? (i.e. before the drive can turn on).
A little clarification with respect to the inputs and outputs would help a lot.
Terry
the inputs that are triggered are prox's. they are on a moving gantry. the contol wires are ran through conduit to a festoon system. there are inputs, outputs and vfd to motor connection in the festoon.
the program is designed that when certain prox's are on at the same time they make it a fault condition.the vfd's are new, everything is new. if i unplug the vfd to motor connections the interference stops. i can watch the input card lights and when the vfd kicks on most all of the prox inputs flickerand registers on the plc. I am using dc inputs---relay outputs
Quick and dirty fix
Use the input wires to pull in relays and then use a set of the relay contacts to drive the input. Induced noise wont pull in the relay. Regards Alan Case
Take a look at the I/O signals with an O-Scope to get an idea of the level of the induced noise. Take a few minutes to try a simple capactive filter and/or reverse biased diode to reduce the noise. Don't spend too much time doing this if it doesn't show immediate results.
Reactors are expensive and take up a lot of space. You may want to run a quick test to demonstrate separate wiring would actually solve the problem. Try running wires from one of the prox's to the PLC and just let them lay on the floor and see if that works. If it does, the best solution would be to separate all the VFD wiring from I/O wiring.
If you are absolutely stuck running things together in a festoon, you may have to switch to fully shielded cables, for motor leads AND control signals (seperate cables, obviously).
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
40
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
170
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
152
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
301
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
398