Vfd

Oh, I just remember one detail that I found irritating with AB PF70 VFD's. I control the drive via a network card, and there is no separate power supply to the network card or the control electronics. Thus cutting the power on the input side promptly triggers a bus fault as well. So it would seem that AB in principle expect a contactor to sit on the output side.

On Siemens MM4 VFD's the network card has a separate power supply, so in stead of a bus fault, you can get a meaningful error message "No input voltage". So it seems that Siemens in principle expect a contactor to sit on the input side.

edit:
Found a picture for Siemens MM4 with the contactor on the input side.
MM4_connections.GIF
 
Last edited:
Breaking the input power to a drive on a typical network, DeviceNet, ControlNet and Ethernet IP does cause a network fault, however after powering the drives back up, they reconnect. We are doing this on every system, with any of the 3 networks listed.
 
Hi all,
thanks a lot for your comments. I really don't know much of the information about contactors. thanks once again for your replies.
 
If it is for safety, be sure to use the SAFE-OFF optional module in the powerflex drive. Don't rely on the standard digital input alone. The safe off option is a tiny relay that kills gate power to the IGBT power modules in the drive when it loses power.


Paul
 

Similar Topics

I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
53
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
174
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
159
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
305
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
13
Views
427
Back
Top Bottom