Vfd

rvitrih

Member
Join Date
Feb 2009
Location
Toronto
Posts
29
Hi,

Just a quick question. I have a bank of 12 identical motors that I need to all run at the same speed through a VFD. Can I connect them all to one VFD in parallel, or is this generally not accepted. It seems less expensive to do it this way.

Thank

Richard
 
You can run all 12 motors on one drive but you will need to add up all of the motor FLA's and add 110%. Size the drive to that ampacity. As already mentioned, you will need an overload block in each motor's leads with the control contacts tied in a closed series loop and run back to the drive as a fault loop.

The motors will not match speed perfectly. You can expect about as much error as the motor nameplate slip. That would typically be 2% or so of base speed. If you need more accuracy than that, you will need to use individual drives for each motor.
 
VFD's

Hi,

The accuracy is not that important, I just need to roughly control the speed. just to clarify you are saying that I need to ties all the overloads together is series, so that a fault in any one motor will trigger the VFD?.

Thanks Richard
 
Another issue is branch circuit protection after the VFD.

With a single motor to a VFD the input fusing to the VFD will protect the downstream wiring. When you use multiple motors on one VFD, the input fusing to the VFD will be too large to protect the downstream wiring.
 
Last edited:
Have done this for years:-
CAUTIONS
1. Install a filter rated for the drive current between the output of the drive and the overloads.
2. You can typically run wiring for up to 3 motors in each conduit.
3. Use a single ground for the drive and run the motor grounds ONLY to the drive ground.
4. Your motor speed will vary much more than the slip based on varying motor sizes and load. Expect at least 10-15% fluctuation.
5. Use inverter rated motors.
 
It will be better if we put the equal length of cables for each motor after the VFD.
But Dear (Bill)Widelto can i know why it is important to run each motor thru separate Conduit
(This is my First Post to Community so plz ignor if there is any Mistake) 📚

-------------------
Pawan Rathi
 
I would run each motor leads in a separate conduit also because
1. Only one can fail. Much easier to fix. Admittedly if one fails then the whole machine goes down.
2. My lack of full understanding of VFD output problems ie spikes, harmonics etc. Seems to me putting more in one conduit will compound problems.

Re question about branch circuit protection
Technically each of 12 motor feeds from VFD is a separate branch (???).
Therefore the branch would need its own overcurrent device which is also able to interrupt a fault current ie short.

With 12 motors on one VFD it seems to be a good question. As suggested insertion of the overloads would be acting to provide overcurrent protection for the individual motors and would be connected to trip the VFD. If there is a major fault ie short circuit the VFD would trip on overcurrent.

BUT the VFD would provide protection at 12 X the "ideal" branch circuit rating.

Is this an adaptation of NEC tapping a feeder rule?

Below NEC articles address grouped motors
NEC 430.87, -53, -24 seem appropriate. Am I missing one. Dont see VFD in index.

Dan Bentler

Dan Bentler
 
The electronic motor overload function of the VFD is useless in your application [it is the individual motor overloads are protecting each motor].
Disable the overload function in the VFD and/or set it at to the maximum possible value [depends on manufacturer of VFD].
Wire the external overloads in series to the Overload input of the drive so that if any one motor trips then the drive shuts off. Enable the external overload input parameter of the VFD.
 
BitsNBytes, I agree with all your comments except motor speed error. There is no reason to believe that the error will exceed normal motor slip which would be about 2%.
 
Hi,

Thanks for all your help. I tried it with 6 motors today and it seemed to work fine. If you have any further information it would still be greatly appreciated.


Thanks

Richard
 

Similar Topics

Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
152
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
146
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
292
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
12
Views
382
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
104
Back
Top Bottom