Vigeo Designer with Redundant PLC
marwan_13
Sep 2006
Amman-Jordan
28
Dear All,
I need to configure the vijoe designer so that the Shneider HMI can communicate with Hot standby (redundant PLC), the communication will be via ethernet.
Any Idea please.
Regards.
Marwan
If it's a Schneider hot standby, the IP addresses swap on fail-over so just point Vijeo Designer to the IP address of the primary. Of course, on swap over, the TCP connection has to be torn down and recreated to the new primary device (which has a different MAC).
Other platforms: not sure how they handle IP addresses on fail-over, so cannot provide any ideas.
can anyone let us know how to configure redundant EtherNet communication in vijeo designer.
What are you trying to do exactly ?
There is no mechanism for a redundant connection in Vijeo Designer that i know of, if you are connecting to a Schneider redundant PLC it's as above, the IP of the PLC swaps at changeover so there is nothing to do at the Vijeo Designer HMI end
Does no 1 use the help files anymore?
Just type redundancy in the vijeo designer help and it will show you
primary and secondary IP address's needs to configure in vijeo????
You wont care what's going on in the Standby PLC, when the CPU's swap over the HMI will drop comms for a second or two, then come back up
If what you want to do is have a redundant connection to the same PLC then that's as below:
Setting Up the Modbus Dual Ethernet Connection
Set up the Modbus TCP/IP device driver. For more information, see Section 5.2.1, Adding a Device Driver.
Configure the communication settings for the driver in the Driver Configuration dialog box. For more information, see Section 5.2.2, Configuring Communication Settings.
Configure the communication settings for the equipment in the Equipment Configuration dialog box. For more information on the Modbus TCP/IP equipment properties, see Section 26.3.6, Changing I/O Manager Communication Settings: Schneider Electric. For the Modbus TCP/IP device driver, you must define the following settings to set up the Modbus dual Ethernet connection:
IP Address – Enter the primary IP address.
Secondary Connection – For a PLC with two Ethernet ports, enable this check box to allow a secondary IP address to be entered.
Backup IP – Enter the secondary IP address.
How do I organize the template for my controls. I am new to Logix Designer but have used RS500 and RS5000. My new Logix Designer has Toolbars...
255
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
136
Good Day all. I am currently busy with a schneider HMI design in vijeo designer and i want to know how you can animate an image to move on the x...
198
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
151
Does anyone know how to set the background colors of instuction blocks (TON, MOV, etc)?
146