wallclocktime issue
asterof
May 2007
Califonia
554
Controllogix firmware 16
L61 CPU
under Controller Properties system time is 9/5/2011
however using the GSV call to the WALLCLOCKTIME
.Day is shown as 9/6/2011
if I change 9/5/2011 to 9/6/2011 then .Day goes to 7
In version 16, the way the Date/Time is calculated from the controller clock was changed.
The WALLCLOCKTIME object is now Universal Coordinated Time, more commonly called "Greenwich Mean Time", or "Zulu Time" if you have a crewcut and good posture.
There are new related objects, including LocalDateTime, which has the option of implementing Daylight Saving Time.
If you're on the East Coast of the USA and posting after 8 PM, it's already after midnight GMT so the Day value of WALLCLOCKTIME will be 1 greater than you expect, but LOCALDATETIME will have the expected Day value.
This change is well described in the v16 Release Notes and in RA Knowledgebase Article ID 37953 (TechConnect).
Thanks for reminding me
I think somewhere I remember that
but use it so little I would have forgotten
Hello, I am doing a PLC5-Contrologix plant migration. So far with the same exact GSV WallClockTime to DateTime array half of my controllers...
1,597
Found a minor error generated on a rung which holds an SSV instruction for WallClockTime. Parameters for the instruction are as follows: Set...
2,627
Hello: Before posting had a look to previous posts for Logix Studio's GSV WallClockTime, but did not see anything that could help me. Would be...
1,887
I am using the GSV bit to retrieve the PLC time, but it says the year is 1970. I haven't been able to find anyway to change the PLC's clock. I'm...
4,580
Hi. I hope you could give me some advise here. I'm ongoing with a project which has many plates that are glued individual and put into a...
2,619