WEG VFD Issues, 400hp motor, and chipper disk

Jasondelane

Lifetime Supporting Member
Join Date
Mar 2015
Location
Florence sc
Posts
221
We are running a high inertia load on a WEG CFW11 VFD.

The motor is 400HP, 60hz, 508 FLA(from memory), 598RPM.

The issue we're having is that the high inertia load is causing DC Bus Overvolts when the chipper is loaded and then unloaded.

The installers had the VFD setup on V/Hz mode. I changed it to Sensorless Vector and did a rotate tune. It seems to accelerate better now but I don't think that helped the issue with overvolts.

I also adjusted the Maximum negative torque value from the default 150% to 4%. This seems to have had the greatest improvement.

I noticed when the chipper is running unloaded it always runs -4% torque for some reason. You would think this would slow the chipper down but that seems to be the "idle adjustment" the VFD is making to maintain 600RPM.

The accel is 60 Sec, Decel is 360 Seconds. The VFD runs -4% torque during the decel also.

When I check the last fault snapshot it's usually around 470 amps (unloaded amps are around 280), 680 DC bus volts.

What are some other settings I can adjust to properly run this setup?
 
You might try turning negative torque limit to 0, but be careful to watch for motor speed. Some drives will run away, and overspeed. Be ready to hit the e-stop!

Also, increasing current Proportional gain and decreasing the Current Integral gain can help with some drives.

I'm only slightly familiar with WEG drives, but it appears to be a decent drive, and MAY be able to handle the high inertia without a DB resistor. Some can, some can't...
 
I don't have WEG experience. Rockwell, Siemens and Mitsubishi all have settings for 'bus voltage' control. I don't know what they do, exactly. But you select PWM first, or Voltage first ... it's a selector.

I have had problems with speed regulation on high inertia fans. When I run them at 60 Hz, I've had to set the maximum running speed to about 65 Hz so that they don't trip on overspeed when the load drops and the torque needs to compensate.

It doesn't appear to hurt anything to have the maximum speed higher than what you are running your load. But it makes a difference to the drive control system.
 
I don't have WEG experience. Rockwell, Siemens and Mitsubishi all have settings for 'bus voltage' control. I don't know what they do, exactly. But you select PWM first, or Voltage first ... it's a selector.

I have had problems with speed regulation on high inertia fans. When I run them at 60 Hz, I've had to set the maximum running speed to about 65 Hz so that they don't trip on overspeed when the load drops and the torque needs to compensate.

It doesn't appear to hurt anything to have the maximum speed higher than what you are running your load. But it makes a difference to the drive control system.

Fuji/GE has a similar setting. The default Max set speed is 60hz, and the default max freq is 70hz. That could be too high for some loads.
 
The OV on a load change is the result of set speed being lower than the actual speed. So under load, the slip is high because the actual rotor speed is being kept LOWER than the commanded speed by the load. So when the load goes away, the drive has not been told to change speed, but the motor actually speeds up. This is what "Slip Compensation" is for. That drive has this feature (P0138) but the factory default setting is Zero. Try increasing it.
 

Similar Topics

Anyone use WEG vfds on here? Thinking of trying CFW300A01P6T2NB20.
Replies
0
Views
771
Hello everyone, Im having the following problem, Speed output of the vfd is always 115hz. If i set the speed reference to 50hz the output still...
Replies
12
Views
3,603
Hi Guys, I just wanted to know your thoughts and opinions on WEG vsd's if you have experience of them? We use them as our goto drive for any...
Replies
14
Views
4,791
Hello, I have an automatic conveyor line and had a company install it at the start of this year. There were unable to set up a dual controller...
Replies
1
Views
607
Hi, I have an application using the PLC TPW03-60HR-A connected with OP08 HMI. It's the first time I'm accessing this application and I don't know...
Replies
1
Views
905
Back
Top Bottom