Weintek cmt error "device server disconnected"

alifarzam

Member
Join Date
May 2021
Location
Lahore
Posts
7
Hello friends!! I am going through a issue... I have comissioned a cmt-svr102 on a site it works fine but after some time like two or three days it will show device server disconnected. and its needs to be reset physically by the reset button from the device otherwise it will not work, I have attached a picture of it if anyone has faced the similar issue please help me out!
WWP7dWG
 
It sounds like the device you are connected to is locking up, or timing out on the com port.

What is the device you are connected to and what type of communications is involved?
 
How can I say that there's no communication problem... It's because those same communications are happening on a SCADA system and another weintek HMI... It's working fine there... Even on CMT communication work fine .. its the cmt device that goes disconnected...
 
OK, I looked closer at your pic and understand.

I don't believe the Easy Access / CMT viewer is going to allow you to stay connected 24/7, but I could be mistaken. You are connecting to Weintek's free VPN service to view the screens on your cmt-svr102, correct? It sounds like your connection to Weintek is getting interrupted but that doesn't explain why the cmt-svr102 has to be reset.
 
Last edited:
Svr doesn't have a local display... It only works remotely via Lan network on cmt viewer... It just goes disconnected after two /three days... It's just a mess for me.
 
The issue arises after downloading in the CMT device... There's a reset button on it... you need to reset it by hand... and it will go fine .. issue will not arise until you download in the HMI again... didn't find any reasonable solution .. I think it's just a problem with HMI firmware... can't do anything else..
 

Similar Topics

I require remote access to my projects that are away from home. I did some homework and decided that Weintek looked to have a good solution. Set...
Replies
1
Views
46
Hello everyone, I am currently facing a challenge while trying to connect two Weintek HMI units with a Mitsubishi FX2N PLC. When connecting a...
Replies
5
Views
542
I have been using two of these HMIs on two sites with similar projects but developed separately. Now i want to use screens from one on the other...
Replies
0
Views
348
Hi, I bought a Weinview/Weintek MT8071ip HMI and an EasyAccess Activation Card. I have activated the card on the HMI (it says activated), but...
Replies
1
Views
913
Hi guys: I'm looking for, the programming software for Weintek MT8150iE, I looked for at Weintek Website, but , I can't find it help me please AD
Replies
5
Views
1,340
Back
Top Bottom