Hi. Can anyone help me out with this one? This something that I am just having hard time figuring out. I understand and can also follow the run logic Rung. But from where (what is controlling) is this Discharge Enable XIC. What is controlling it, Where do I look further. I followed it back as far as I can back to the Definition AOI. But what is the real world instant that controls it to make the output MTR (OTE) true. I might be over thinking but I am at a loss. Thank you all.
Right click on the AOI & select Properties
In the popup go to the Parameters tab. You may have to scroll over or widen the window.
Click on Vis and the parameter will be visible in the call.
Click on Req and it will become a required parameter to address in the call, and Vis will automatically check itself.
I have nothing. :angr:
Is the instance of the AOI UT_JAM?
If so, where in the main or other is the call for the AOI? at the call, it would have some tag listed for the DISCH_EN. Otherwise, somewhere else in the program you may have UT_JAM.DISCH_EN being set to something.
You need to go to the block call for that specific control.
Where the drop down is in your first picture select the call you need. Then to the right of the drop down there is a little button to go to block call. Hover over for tool tip. Click it, it will take you to the parent routine where the AOI is being used. Since the parameter is required it will be displayed inside the AOI call. Underneath this is the tag passing a value to this call of the AOI.
I would check for that bit being used on a HMI somewhere.
The description says to me that that part can be turned on or off, and I would do that on the HMI, on an engineering page or something.
Cheers
Mark
Hi all. Never really noticed, but I started double checking operands in the CPT instruction. I found if I have the expression N7[37,1] - N7[35,1]...
134
All, I am trying to reset timers when a Work Order change occurs. The Work Order comes in as a string and I am comparing it to a tag...
107
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
237
Hi, I'm having an issue in crimson 3.0 when I create a programme using a case statement referencing a fault word that each bit needs to change the...
301
Has anyone ever seen where you have a tag reading from the plc in scada. In this instance it's just a PEC, I set it up on one scada terminal and...
115